Guidelines for AC-powered equipment
An AC-powered installation must meet these requirements:
• Use a 15 amp external branch circuit protection device to install the unit.
• Use one power feed for each individual power supply.
Caution: Customers should not attempt to replace batteries. There is a risk of explosion if a battery
is replaced with an incorrect type. Field technicians should dispose of used batteries according to
the instructions.
Attention: Il y a risque d'explosion si la batterie est remplacée par une batterie de type incorrect.
Mettre au rebut les batteries usagées conformément aux instructions.
Important: The platform must be installed in a RESTRICTED ACCESS LOCATION, such as a
central office or customer premises environment.
Note: The following guidelines apply to STATIONARY PLUGGABLE EQUIPMENT TYPE A with
simultaneous multiple connections to the AC MAINS SUPPLY:
• The building installation shall provide a means for connection to protective earth; and
• The equipment is to be connected to that means; and
• A SERVICE PERSON shall check whether or not the socket-outlet from which the equipment is
to be powered provides a connection to the building protective earth. If not, the SERVICE
PERSON shall arrange for the installation of a PROTECTIVE EARTHING CONDUCTOR from
the separate protective earthing terminal to the protective earth wire in the building.
Note: High leakage current. Earth connection essential before connecting supply.
21