108
Function assignment of external
terminal and control
14 114 FDN PID lower limit
Output when the feedback value falls below
the lower limit of PID control.
Pr. 127 to Pr. 134,
Pr. 575 to Pr. 577
20115 115 FUP PID upper limit
Output when the feedback value rises above
the upper limit of PID control
16 116 RL
PID forward/reverse
rotation output
Output when forward rotation is performed in
PID control.
17  MC1
Commercial power-
supply switchover MC1
Used when the commercial power supply-
inverter switchover function is used.
Pr. 135 to Pr. 139,
Pr. 159
20918  MC2
Commercial power-
supply switchover MC2
19  MC3
Commercial power-
supply switchover MC3
25 125 FAN Fan fault output Output at the time of a fan fault. Pr. 244 216
26 126 FIN
Heatsink overheat
pre-alarm
Output when the heatsink temperature
reaches about 85% of the heatsink overheat
protection providing temperature.
 242
45 145 RUN3
During inverter
running and start
command is on
Output when the inverter running and start
commands are on.
 109
46 146 Y46
During deceleration at
occurrence of power
failure (retained until
release)
Output when the power failure-time
deceleration function is executed.
Pr. 261 to Pr. 266
130
47 147 PID
During PID control
activated
Output during PID control.
Pr. 127 to Pr. 134,
Pr. 575 to Pr. 577
201
64 164 Y64 During retry Output during retry processing. Pr. 65 to Pr. 69 132
70 170 SLEEP
PID output
interruption
Output when the PID output interruption
function is executed.
Pr. 127 to Pr. 134,
Pr. 575 to Pr. 577
201
90 190 Y90 Life alarm
Output when any of the control circuit
capacitor, main circuit capacitor and inrush
current limit circuit or the cooling fan
approaches the end of its service life.
Pr. 255 to Pr. 259
217
91 191 Y91
Alarm output 3
(power-off signal)
Output when an error occurs due to the circuit
failure or connection alarm of the inverter.
 110
92 192 Y92
Power saving
average value
updated timing
Turned on and off alternately every time the
power saving average value is updated
when the power saving monitor is used.
Cannot be set to Pr. 195 and Pr. 196 (relay
output terminal).
Pr. 52, Pr. 54,
Pr. 158, Pr. 891 to
Pr. 899
137
93 193 Y93
Current average
value monitor signal
Average current value and maintenance
timer value are output as pulses.
Cannot be set to Pr. 195 and Pr. 196 (relay
output terminal).
Pr. 555 to Pr. 557
220
94 194 ALM2 Alarm output 2
Output when the inverter's protective
function is activated to stop the output
(major fault). Continue outputting the signal
during inverter reset and stop outputting
after reset is cancelled.
*2
 109
95 195 Y95
Maintenance timer
signal
Output when Pr. 503 rises to or above the Pr.
504 setting.
Pr. 503, Pr. 504 219
96 196 REM Remote output
Output to the terminal when a value is set to
the parameter.
Pr. 495 to Pr. 497
114
98 198 LF Minor fault output
Output when a minor fault (fan failure or
communication error warning) occurs.
Pr. 121, Pr. 244
177,
216
99 199 ALM Alarm output
Output when the inverter's protective function is
activated to stop the output (major fault). The
signal output is stopped when a reset turns on.
 109
9999  No function 
*1 Note that when the frequency setting is varied using an analog signal or of the operation panel (FR-DU07), the output of the SU (up to
frequency) signal may alternate on and off depending on that varying speed and the timing of the varying speed due to acceleration/
deceleration time setting. (The output will not alternate on and off when the acceleration/deceleration time setting is "0s".)
*2 When a power supply reset is performed, the alarm output 2 signal (ALM2) turns off as soon as the power supply switches off.
Setting
Signal
Name
Function Operation
Related
Parameters
Refer
to Page
Positive
Logic
Negative
Logic