117
Monitor display and monitor output signal
4
PARAMETERS
Converter output
voltage
0.1V 8
*1
8
200V
class:400V
400V
class:800V
Displays the DC bus voltage value.
Regenerative
brake duty
0.1% 9
*1
9
Pr. 70
Brake duty set in Pr. 30 and Pr. 70 (Setting
can be made for the 75K or more.)
Electronic thermal
relay function load
factor
0.1% 10
*1
10 100%
Displays the motor thermal cumulative value
on the assumption that the thermal operation
level is 100%.
Output current
peak value
0.01A/0.1A
*5
11
*1
11
Pr. 56
Retain the peak value of the output current
monitor and display (clears at every start)
Converter output
voltage peak value
0.1V 12
*1
12
200V
class:400V
400V
class:800V
Retain the peak value of the DC bus voltage
value and display (clears at every start)
Input power
0.01kW/
0.1kW
*5
13
*1
13
Rated
inverter
power
× 2
Displays power of the inverter input side
Output power
0.01kW/
0.1kW
*5
14
*1
14
Rated
inverter
power
× 2
Displays power of the inverter output side
Load meter
0.1%
17 17 100%
Torque current is displayed in % on the
assumption that the Pr. 56 setting is 100%
Cumulative
energization time
*2
1h 20
×
Cumulative energization time since the
inverter shipment is displayed
You can check the numbers of the monitor
value exceeded 65535h with Pr. 563.
Reference voltage
output
21
Terminal FM:1440 pulse/s is output
Terminal AM: 10V is output
Actual operation
time
*2*3
1h 23
×
Cumulative inverter running time is displayed.
You can check the numbers of the monitor
value exceeded 65535h with Pr. 564.
Use Pr. 171 to clear the value.
(Refer to page 120 .)
Motor load factor 0.1% 24 24 200%
On the assumption that the rated inverter
current value is 100%, the output current
value is displayed in %.
Monitor value = loutput current monitor
value/rated inverter current
× 100 [%]
Cumulative power
0.01kWh/
0.1kWh
*4, *5
25
×
Cumulative power amount is displayed
according to the output power monitor
Use Pr. 170 to clear the value.
(Refer to page 120.)
Power saving
effect
Variable
according
to
parameters
50 50
Inverter
capacity
Displays energy saving effect monitor
You can change the monitor to power saving,
power saving average value, charge display
and % display using parameters.
(For details, refer to page 138.)
Cumulative saving
power
51
×
PID set point 0.1% 52 52 100%
Displays the set point, measured value and
deviation during PID control
(For details, refer to page 206.)
PID measured
value
0.1% 53 53 100%
PID deviation 0.1% 54
×
Input terminal
status
55
*1
×
ON/OFF status of the input terminal is
displayed on the PU
(Refer to page 119 for DU display)
Output terminal
status
*1
×
ON/OFF status of the output terminal is
displayed on the PU
(Refer to page 119 for DU display)
Option input
terminal status
56
××
ON/OFF status of the input terminal of the
digital input option (FR-A7AX) is displayed
on the DU (refer to page 119 for details)
Option output
terminal status
57
××
ON/OFF status of the output terminal of the
digital output option (FR-A7AY) and relay
output option (FR-A7AR) is displayed on the
DU (refer to page 119 for details)
Types of Monitor Increments
Pr. 52 Parameter
Setting Value
Pr. 54 (FM)
Pr. 158 (AM)
Parameter
Setting
Value
Full-scale
value of the
terminal FM
and AM
Description
DU LED
PU main
monitor