145
Frequency setting by analog input (terminal 1, 2, 4)
4
PARAMETERS
(2) Perform operation by analog input voltage
The frequency setting signal inputs 0 to 5VDC (or 0 to 10VDC) to across
the terminals 2-5. The 5V (10V) input is the maximum output frequency.
The maximum output frequency is reached when 5V (10V) is input.
The power supply 5V (10V) can be input by either using the internal
power supply or preparing an external power supply. The internal power
supply outputs 5VDC across terminals 10-5, or 10V across terminals
10E-5.
When inputting 10VDC to the terminal 2, set any of "0, 2, 4, 10, 12, 14"
in Pr. 73. (The initial value is 0 to 5V)
Setting "1 (0 to 5VDC)" or "2 (0 to 10VDC)" in Pr. 267 changes the
terminal 4 to the voltage input specification. When the AU signal turns
on, the terminal 4 input becomes valid.
(3) Perform operation by analog input current
When the pressure or temperature is controlled constant by a fan, pump,
etc., automatic operation can be performed by inputting the output signal
4 to 20mADC of the adjuster to across the terminals 4-5.
The AU signal must be turned on to use the terminal 4.
Setting any of "6, 7, 16, 17" in Pr. 73 changes the terminal 2 to the
current input specification. At this time, the AU signal need not be turned
on.
Compensation input characteristic
when STF is on
(4) Perform forward/reverse rotation by analog input
(polarity reversible operation)
Setting any of "10 to 17" in Pr. 73 enables polarity reversible operation.
Providing ± input (0 to ±5V or 0 to ±10V) to the terminal 1 enables
forward/reverse rotation operation according to the polarity.
Parameters referred to
Pr. 22 Stall prevention operation level Refer to page 73
Pr. 125 Terminal 2 frequency setting gain frequency, Pr. 126 Terminal 4 frequency setting gain frequency Refer to page 148
Pr. 252, Pr. 253 Override bias/gain Refer to page 146
STF
Inverter
Forward
rotation
Frequency
setting
0 to 5VDC
10
2
5
Connection diagram using
terminal 2 (0 to 5VDC)
SD
STF
Inverter
Forward
rotation
Frequency
setting
0 to 10VDC
10E
2
5
Connection diagram
using terminal 2 (0 to 10VDC)
SD
Terminal
Inverter Built-in Power
Supply Voltage
Frequency Setting
Resolution
Pr. 73 (terminal 2
input voltage)
10 5VDC 0.030Hz/60Hz 0 to 5VDC input
10E 10VDC 0.015Hz/60Hz 0 to 10VDC input
REMARKS
The wiring length of the terminal 10, 2, 5 should be 30m maximum.
STF
Inverter
Forward
rotation
Frequency
setting
4
5
AU
Connection diagram using
terminal 4 (4 to 20mADC)
4 to 20mADC
Current
input
equipment
SD
Not reversible
Forward
rotation
Reverse
rotation
Reversible
Terminal 1 input (V)
+5
(+10)
-5
(-10)
0
60
Set frequency