210
Special operation and frequency control
(1) Connection diagram
The following shows the connection diagram of a typical electronic bypass sequence. Sink logic, Pr. 185 = "7", Pr.
192 = "17", Pr. 193 = "18", Pr. 194 = "19"
Operations of magnetic contactors (MC1, MC2, MC3)
Electronic bypass sequence connection diagram
*1 Take caution for the capacity of the sequence output terminal.
The used terminal changes depending on the setting of Pr. 190 to
Pr. 196 (output terminal function selection).
*2 When connecting a DC power supply, insert a protective diode.
When connecting an AC power supply, connect a relay output
option (FR-A7AR) and use a contact output.
*3 The used terminal changes depending on the setting of Pr. 180 to
Pr. 189 (input terminal function selection).
CAUTION
Use the electronic bypass operation function in external operation mode. Be sure to connect the other power supply since the
function is not performed normally unless the connection terminals R1/L11, S1/L21 are not connected to the other power supply
(power supply that does not pass MC1).
Be sure to provide mechanical interlocks for MC2 and MC3
.
Magnetic
Contactor
Installation Place
Operation ({: Shorted, ×: Open)
Bypass operation
During inverter
operation
At an inverter alarm
occurrence
MC1
Between power supply and
inverter input
{{
×
(Shorted by reset)
MC2
Between power supply and
motor
{
×
×
(Can be selected using
Pr. 138, always open
when external thermal
relay is on)
MC3
Between inverter output and
motor
×
{
×
Inverter start
(forward rotation)
MC1
R/L1
S/L2
T/L3
STF
R1/L11
S1/L21
CS
MRS
RES
10
2
5
U
V
W
External
thermal relay
IM
(MC1)IPF
(MC2)OL
SE
MC3
MC2
24VD
C
MC
1
External
thermal reset
Frequency
setting signal
(MC3)FU
Inverter/electronic
bypass operation
interlock
MC
2
MC
3
*3
*1
*2
*1
*1
JOG(OH)
MCCB
MC2
MC3
SD
Output Terminal Capacity
Output Terminal
Permissble Load
Inverter open collector output
(RUN, SU, IPF, OL, FU)
24VDC 0.1A
Inverter relay output (A1-C1, B1-
C1, A2-B2, B2-C2)
Relay output option (FR-A7AR)
230VAC 0.3A
30VDC 0.3A