point offset
point offset1.9.8
change in curve
outdoor temp. point
°C
°C
outdoor temp. °C
flow temperature °C
outdoor temp. point
Setting range: -40 30 °C
Default value: 0 °C
change in curve
Setting range: -10 10 °C
Default value: 0 °C
Menu
1.9.8
Select a change in the heating curve at a certain outdoor temperature
here. One step is usually enough to change the room temperature by one
degree, but in some cases several steps may be required.
The heat curve is affected at ± 5 °C from set outdoor temp. point.
It is important that the correct heating curve is selected so that the room
temperature is experienced as even.
TIP
If it is cold in the house, at, for example -2 °C, "outdoor temp. point" is
set to "-2" and "change in curve" is increased until the desired room
temperature is maintained.
Caution
Wait 24 hours before making a new setting, so that the room temperat-
ure has time to stabilise.
night cooling
night cooling1.9.9
min diff. outdoor-exhaust
start temp. exhaust air
°C
°C
night cooling
start temp. exhaust air
Setting range: 20 30 °C
Default value: 25 °C
min diff. outdoor-exhaust
Setting range: 3 10 °C
Default value: 6 °C
Menu
1.9.9
NIBE™ F370Chapter 3 | F370 at your service40