SPECIFICATION
DATA
Check Air Cleaner Operation
With all components in place, turn on air cleaner switch and energize system blower. Check following points
of operation:
1. The neon light next to the On-Off switch is on. The neon light shows that the air cleaner is energized and the
high voltage power supply is working correctly.
2. Turn off the system blower. The neon light should go off after a few seconds.
3. Turn on the system blower. With the air cleaner energized, push the test button. A snapping sound indicates
that the collector voltage is present on the cell.
4. With a multispeed blower, repeat steps 1 through 3 for each fan speed.
Maintenance
The air cleaner must be cleaned when pressure drop across the air cleaner reaches 0.5 in. w.c. (0.1 kPa), or at
least annually. If the air cleaner is installed downstream from an atomizing humidier or if the installation includes
both heating and cooling, more frequent replacement may be necessary. Clogged prelters must be cleaned
promptly to avoid restricting airow and reducing efciency of the heatingcooling system. Record the maintenance
date in the space provided on the Electronic Air Cleaner Wash Reminder and Postlter Replacement Schedule.
Specications
The specications in this publication do not include normal manufacturing tolerances; therefore, an individual unit
may not exactly match the listed specications. This product is tested and calibrated under closely controlled
conditions, and some minor differences in performance can be expected if those conditions are changed.
Fractional Efciency
Efciency Ratings: Efciency ratings are based on American Society of Heating, Refrigerating and Air
Conditioning Engineers Standard 52.2-1999. Efciency ranges are dened for small particles, E1 =.3 to 1.0
micron; medium particles, E2 = 1.0 to 3.0 microns; and large particles, E3 = 3.0 to 10.0 microns.
Table 5. Fractional Efciency With and Without Postlter.
With Postlter Without Postlter
E1 = Up to 81% at 492 fpm. E1 = Up to 73% at 492 fpm.
E2 = Up to 93% at 492 fpm. E2 = Up to 88% at 492 fpm.
E3 = Up to 99% at 492 fpm. E3 = Up to 95% at 492 fpm.
F300 Electronic Air Cleaner 68-0240EF—07
14
68-0240EF_B.indd 14 9/14/11 3:04 PM

Table of Contents

Other manuals for Honeywell F300

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the Honeywell F300 and is the answer not in the manual?

Honeywell F300 Specifications

General IconGeneral
TypeElectronic Air Cleaner
Voltage120V
Filter TypeElectronic
Warranty5 year limited warranty
Collection CellAluminum
Pre-filterWashable
Wattage15W

Related product manuals