Page 8 of 11 06/10/17
07-09
0
0-3
Stop method:
0: Deceleration to stop
1: Coast to stop
2: DC injection braking
3: Run signal inhibit (timer) during Coast to
stop
02-01
**A
10%~200% of
rated current (V/f)
25%~200% of rated
current (SLV)
Motor rated current (for Motor overload
protection)
13-08
0
0-10
Factory Reset: Inverter Supply voltage.
2: 2 wire initialization(220/440V,60Hz)
3: 3 wire initialization(220/440V,60Hz)
4: 2 wire initialization(230/415V,50Hz)
5: 3 wire initialization(230/415V,50Hz)
6: 2 wire initialization(200/380V,50Hz)
7: 2 wire initialization(200/380V,50Hz)
8: PLC initialization
9: 2 wire initialization(230/460V,60Hz)
10: 3 wire initialization(230/460V,60Hz)
Note:- For Full Parameter List see the Instruction manual
Control Modes & Auto Tune
F510 provides three control modes.
Select the relevant control mode for the application.
Default control mode is V/f.
V/f can be used for most applications specifically multi-motor
or applications where auto tune is not successful
or when a customized v/f pattern may be required.
Several V/f patterns are available selectable by parameter 01-00.
Select the appropriate one based on the application load type and the motor base frequency of
50 or 60 Hz.
For selections of the V/f patterns, Refer to the instruction manual.
Sensorless Vector mode SLV is used for obtaining best performance from a motor.
V/f Mode Parameters
Parameter
Default
Range
Note
01-00
F
0-FF
F: General Purpose. 60Hz system
0: General Purpose. 50Hz system
For full list of preset patterns set by 01-00,
refer to the manual.
FF: Customized V/f.
Set parameters 01-02 to 01-13