TECO F510 Inverter
Quick Start Guide
1) Ensure that the Inverter & the motor have the correct KW power and voltage
ratings.
Motor full load amps must not exceed the Inverter rating.
2) Ensure that the supply & Motor cables are connected correctly prior to
power up.
3) Connect supply cable to terminals R/L1, S/L2, T/L3
4) Connect motor cable to terminals U/T1, V/T2, W/T3
(Swap two leads if motor runs in reverse direction).
5) Connect supply Earth and the motor Earth to the drive Earth
terminal.
Note:-
I ) For detailed installation
and wiring refer to the
Instruction
manual.
This guide is to assist you in installing and running the inverter and verify that it is
functioning correctly for it’s main and basic features.
For detailed information and if there are any doubts please refer to the instruction manual.
Step 1
Supply & Motor connection
Question and Answer IconNeed help?

Do you have a question about the TECO F510 and is the answer not in the manual?

TECO F510 Specifications

General IconGeneral
Control ModeV/F Control, Sensorless Vector Control
Output Voltage3-phase 0 ~ Input voltage
Cooling MethodForced Air Cooling
Storage Temperature-20°C ~ +60°C
Enclosure RatingIP20
Input Voltage3-phase 380 ~ 480V
Output Frequency0~400Hz
Protection FunctionsOvercurrent, Overvoltage, Undervoltage
Braking UnitBuilt-in
CommunicationRS485, Modbus
Rated PowerVaries by model
Overload Capacity150% for 60 seconds
Operating Temperature-10 to 50°C
Humidity95% RH or less (non-condensing)
AltitudeUp to 1000m (derating above 1000m)

Summary

Step 1 Supply & Motor connection

Step 2 Apply power to the drive

Step 3 Test run from keypad

Step 4 To alter frequency from keypad

Remote speed reference and Remote run

Step 1 Remote mode wiring. Speed reference.

Configure remote speed reference and wiring using analog inputs AI1/AI2.

Step 2 Remote mode Run

Set up remote run signal type (PNP/NPN) and connect remote start switch.

Step 3 Check/ verify and alter parameters

Verify and modify parameters for remote start and frequency control.

Step 4 RUN using remote speed reference

Activate remote run switch and control frequency via remote speed reference.

How to alter Parameters from keypad

Basic Quick Start Parameter List

Control Modes & Auto Tune

SLV Mode set parameters in parameter Group 17

Group 17 Automatic Tuning Function Group

Details parameters and options for automatic tuning of the inverter motor.

Wiring Diagram

Related product manuals