Remote speed reference and Remote run
1) Ensure that you have carried out installation & wiring requirements as
per step1 quick start guide on previous page before you proceed.
Two analogue inputs are available. AI1 & AI2
Ensure 00-07 = 0 ( Default= Main frequency source).
2) Select AI1 or AI2 as required.
Voltage only Input. Speed command
Multi-function analog input terminal.
Use SW2 to switch voltage or current input
Settings for AI1:
Set 00-05=1
Settings for AI2 :
Set 00-05 = 7 ( AI2 Aux frequency)
Set 04-05 = 0 ( Default) . Aux frequency.
Set 04-00 = 0 for ( 0-10v or 0-20mA)
Set 04-00 = 1 for ( 2-10v or 4-20mA)
3) Connecting Remote Potentiometer:
Terminal +10V Supply for use with the potentiometer.
Terminal GND 0Vdc
Terminal AI1 or AI2 Potentiometer wiper connection.
4) Connecting Remote 0-10V or 4-20mAc signal
Use terminals AI1 or AI2 as required.
Connect the 0 V of the analogue input signal to Terminal GND .
Remote mode wiring. Speed reference.