TECO F510 - Step 2 Remote mode Run; Step 3 Check; verify and alter parameters; Step 4 RUN using remote speed reference

TECO F510
11 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Loading...
Page 4 of 11 06/10/17
How to alter parameters
Step 2
Remote mode Run
1) Remote Run signal can be either a PNP or NPN input type.
Set PNP or NPN selection as required by SW3.
Note : PNP (positive voltage switching) selection is recommended
for use in EU.
2) Connect remote start switch if required according to diagram in the
instruction manual.
Terminal 24V & S1 (Forward run)
Terminal 24V & S2 (Reverse run)
24V is the common terminal for PNP type inputs.
24VG (0Vdc) terminal is common for the NPN type inputs.
Step 3
Check/ verify and alter parameters
Check / verify and alter parameters for remote start & remote frequency as
necessary before you proceed. Parameters 00-02 & 00-05
See quick start parameter list & How to alter parameters.
Step 4
RUN using remote speed reference.
(Potentiometer, 0-10Vdc or 4-20mA)
1) To run. Activate the remote run switch connected to terminals
S1 (FWD) or S2 (REV) as required. Parameter 00-02 =1
The frequency will ramp up to the frequency set from keypad or
analogue inputs 1 & 2.and according to the set acceleration ramp
time.
2) To Stop. De-activate the remote run switch.
The frequency will ramp down to zero and according to decel ramp
time.