How to alter parameters
1) Remote Run signal can be either a PNP or NPN input type.
Set PNP or NPN selection as required by SW3.
Note : PNP (positive voltage switching) selection is recommended
for use in EU.
2) Connect remote start switch if required according to diagram in the
instruction manual.
Terminal 24V & S1 (Forward run)
Terminal 24V & S2 (Reverse run)
24V is the common terminal for PNP type inputs.
24VG (0Vdc) terminal is common for the NPN type inputs.
Check/ verify and alter parameters
Check / verify and alter parameters for remote start & remote frequency as
necessary before you proceed. Parameters 00-02 & 00-05
See quick start parameter list & How to alter parameters.
RUN using remote speed reference.
(Potentiometer, 0-10Vdc or 4-20mA)
1) To run. Activate the remote run switch connected to terminals
S1 (FWD) or S2 (REV) as required. Parameter 00-02 =1
The frequency will ramp up to the frequency set from keypad or
analogue inputs 1 & 2.and according to the set acceleration ramp
time.
2) To Stop. De-activate the remote run switch.
The frequency will ramp down to zero and according to decel ramp
time.