Troubleshooting
If the operational interference is not shown in the display the following
tips can be used.
Basic actions
Start by checking the following possible fault sources:
That the display is lit or that the supply cable to F110 is connected.
Group and main fuses of the accommodation.
The property's earth circuit breaker.
Low hot water temperature or a lack of hot water
Large hot water consumption.
Wait until the hot water has heated up. Temporarily increased hot
water capacity (temporary lux) can be activated in menu 2.1.
Too low hot water setting.
Enter menu 2.2 and select a higher comfort mode.
Low or a lack of ventilation (exhaust air installation)
See section "Low or a lack of ventilation".
Applies to incoming air blocked (outdoor air installation)
Clean the grille.
Filter blocked (installation with ambient air)
Clean or replace filter (see page 18).
Too low thermostat setting
Low or a lack of ventilation (exhaust air installation)
The ventilation is not adjusted.
Order ventilation adjustment.
Filter blocked.
Clean or replace filter (see page 18).
Exhaust air device blocked or throttled down too much.
Check and clean the exhaust air devices.
Fan speed in reduced mode.
Enter menu 1 and select “normal".
High or distracting ventilation (exhaust air installation)
The ventilation is not adjusted.
Order ventilation adjustment.
Fan speed in forced mode.
Enter menu 1 and select “normal".
Filter blocked.
NIBE™ F110Chapter 4 | Disturbances in comfort34