Caution
If you choose to switch off hot water production during the vacation
“periodic increase" (preventing bacterial growth) are blocked during
this time. "periodic increase" started in conjunction with the vacation
setting being completed.
Caution
If the exhaust air temperature falls below 16 °C, the compressor is
blocked and the electrical addition is permitted to intervene. When the
compressor is blocked heat is not recovered from the exhaust air.
advanced
advanced 4.9
auto mode setting
factory setting user
schedule blocking off
Menu advanced has orange text and
is intended for the advanced user. This
menu has several sub-menus.
Menu
4.9
auto mode setting
stop heating
stop additional heat
filtering time
°C
°C
hrs
auto mode setting4.9.2
stop heating
Setting range: -20 40 °C
Default values: 20
stop additional heat
Setting range: -25 40 °C
Factory setting: 15
filtering time
Setting range: 0 48 h
Default value: 24 h
Menu
4.9.2
When the operating mode is set to "auto", the heat pump selects when
start and stop of additional heat and heat production is permitted, depend-
ent on the average outdoor temperature.
Select the average outdoor temperatures in this menu.
NIBE™ F370Chapter 3 | F370 at your service60