15
BURNER ADJUSTMENT TABLES
NON-RETROFIT APPLICATIONS
If this burner is being installed in a packaged unit (i.e. Burner comes with a boiler or furnace), follow the
installation and set-up instructions supplied with the heating appliance, as settings will differ from those
shown in this manual.
MODEL F3 BURNER SETUP CHART
MODEL F5 BURNER SETUP CHART
1
ACTUAL FIRING
RATE 5% ±
2
NOZZLE
SIZE
3
PUMP
PRESSURE
US GPH GPH PSI BAR
4
TURBULATOR
SETTING
5
AIR DAMPER
SETTING
0.75 .60 x 60/ 80º 145 10 0.0 2.25
0.85 .65 x 60/ 80º 145 10 0.5 2.5
1.00 .85 x 60/ 80º 145 10 1.0 2.75
1.10 1.00 X 60/ 80° 145 10 2.0 3.0
1.25 1.10 x 60/ 80º 145 10 2.5 3.5
1.50 1.25 x 60/ 80º 145 10 3.0 4.25
1.65 1.35 X 60/ 80° 145 10 4.0 6.0
NOTE: The above set up charts are a starting point only. The burner and appliance must be properly set
up using proper combustion testing equipment.
Note: any approved oil burner nozzle type, angle and manufacturer maybe used, as long as input
is corresponding the correct BTU/hr. or US gph input rating of the appliance.
COMBUSTION CHAMBER
Follow the instructions furnished by the boiler/furnace manufacturer. Size retrofit application according to the
appropriate installation codes (e.g. CSA B139 or NFPA #31).
1
ACTUAL FIRING
RATE 5% ±
2
NOZZLE
SIZE
3
PUMP
PRESSURE
US GPH GPH PSI BAR
4
TURBULATOR
SETTING
5
AIR DAMPER
SETTING
0.50 .40 x 60º/80º 160 11.0 0.0 2.3
0.60 .50 x 60º/80º 150 10.4 0.5 2.7
0.75 .60 x 60º/80º 150 10.4 1.5 3.4
0.80 .65 x 60º/80º 150 10.4 2.0 3.6
0.95 .75 x 60º/80º 160 11.0 3.0 4.3