C6501010 STANDARD F3-5 MANUAL Rev. 3-2 10/12/2006
9
APPLICATION FIELD WIRING
REMOTE SENSING OF SAFETY LOCKOUT: The SAFETY SWITCH in the 530SE CONTROL BOX is
equipped with a contact allowing remote sensing of burner lockout. The electrical connection is made at
terminal 4 (•) on the SUB-BASE. Should lockout occur the 530SE CONTROL BOX will supply a power source
of 120Vac to the connection terminal. The maximum allowable current draw on this terminal (4) is 1 Amp.
WARNING: If a neutral or ground lead is attached to this terminal, the CONTROL BOX on
the burner will be damaged should lockout occur.
N
L
HOT LINE (BLACK)
EARTH GROUND (GREEN)
NEUTRAL (WHITE)
LINE SAFETY
SWITCH
OPERATING
LIMIT SWITCH
SAFETY
LIMIT SWITCH
FUSE 15A
N
L
T
T
NEUTRAL (WHITE)
HOT LINE (BLACK)
EARTH GROUND (GREEN)
LINE SAFETY
SWITCH
OPERATING
LIMIT SWITCH
SAFETY
LIMIT SWITCH
FUSE 15A
24
V
AC
120
V
AC
120
V
AC
DIRECT LINE
VOLTAGE LOW VOLTAGE
TRANSFORMER &
SWITCHING RELAY
1 2 43 765 98
N
L
MOTOR
CAPACITOR
BLACK
COIL
BLUE
BROWN
BLACK
VALVE
BLUE
WHITE
BLACK
BROWN
WHITE
WHITE
RIELLO
FACTORY
WIRED SUB
BASE