2903223
7
GB
APPLICATION FIELD WIRING
INSTALLATION NOTE:
ELECTRONIC AIR SHUTTER REQUIRES A CONSTANT
120V POWER SUPPLY TO THE AUX TERMINAL, FAIL-
URE TO PROVIDE THIS WILL RESULT IN NO BURNER
OPERATION OR AIR SHUTTER WILL NOT CLOSE.
PLEASE NOTE: OPERATING LIMIT AND SAFETY LIMIT
ARE TWO SEPARATE LIMITS.
Key to lay-out:
1 - Main disconnect fuse
2 - Manual service switch
3 - Safety limit device
4 - Operating limit device
5 - Earth ground connection burner chassis
6 - Burner control remote lock out alarm device - wired &
supplied by others
AUX - Auxiliary bub base add-on connector (air shutter)
MIN. WIRE SIZE:
INSULATED 18 AWG SOLID OR 16 STRD. RAT-
ED 105° C
PROPER EARTH GROUNDING MEANS REQUIRED ALL WIRING SHOWN PROVIDED BY OTHER.
WIRING DIAGRAM SHOWN FOR STANDARD
RIELLO 530 SE/C PRIMARY CONTROL BOX.
WARNING:
DO NOT activate burner until proper oil line connections have been made, or failure of the pump shaft seal
may occur.
DO NOT activate burner until all safety and operating controls have been wired in series with the burner, as
required by local code authorities and/or as specified by the appliance manufacturer.
AIR SHUTTER
MOTOR
20101944
WARNING