4 - WATER CONNECTIONS
4.4.3 Coil rotation for connections on RIGHT
loosen the four screws that fix the lower exchanger (fig.
4.7 rif. C);
remove the battery water probe;
remove the exchanger (fig. 4.7 rif. F);
remove the drip-collector extension from the central tray
(fig. 4.7 rif. D);
on the opposite side remove the plug on the condensation
evacuation hole (fig. 4.7 rif. E);
loosen the central condensation collection tray fixing
screw (fig. 4.7 rif. G), move the tray and rest it on the
opposite side so that the fixture mouth for the dripcollector
extension comes out of the structure, and block the tray with
the screw previously removed;
re-insert the drip-collector extension and the plug on the
opposite side;
rotate the exchanger moving the fixtures to the opposite
side, and reinsert it on the machine;
tighten all the fixing screws of the exchanger
When all the operations described have been completed,
remount all the components dismounted previously following
the dismounting operations in the opposite order.