INOV8 Model F240 – Edited September 2008
40
Oil Temperature & Pressure Settings
The INOV8 burner has been tested to burn fuel oils up to #6, and a variety of used
petroleum based shop and vehicle oils. Testing has also been done on a variety of
vegetable based oils, such as corn, soybean, and canola oils – both used and new. All of
these oils make potential fuels but have different BTU values and flashpoints that require
adjustments to the burner pressure and preheat temperature. It’s also important to be
aware that the preheat temperature showing on the LED readout is the temperature of
the steel block in the module and not the direct temperature of the oil – which can be 30
o
to 50
o
F higher than the steel block temperature. If the oil being burned is not standard
waste crankcase oil, oil analysis will determine the flashpoint and BTU value for proper
setting of the oil temperature and pressure settings. The settings below are typical:
Type of Oil
*BTU/Gal
* Flashpoint
in degrees F
Oil **
Pressure
SP1
Setting
SP2
Setting
Petroleum based oils
Used crankcase - regular
147,000 240 - 350 9 140 110
Used crankcase –
synthetic
140,000 440 - 507 11 170 110
Used crankcase with 10%
gas
144,500 180 10 140 110
Used crankcase with 20%
gas
142,000 120 10 Off Off
90W gear lube
144,000 250 - 300 10 150 110
Transmission fluid
143,000 340 - 400 10 140 110
Hydraulic oil
144,000 336 10 140 110
Mineral oil
138,000 325 - 400 12 160 120
Mineral spirits
136,000 115 12 Off Off
Jet fuel – JP 4
141,000 100 - 128 11 Off Off
Fuel oil - #2 & diesel
140,000 126 12 Off Off
Non-petroleum based oils
B100
130,000 130 13 Off Off
Crude soy
140,000 650 11 170 120
Glycerin (sample 1)
102,000 320 13 170 120
Glycerin (sample 2)
111,000 70 13 Off Off
Used cooking oil
133,000 400 - 650 13 170 120
* Flashpoints and BTU values have been obtained from US Oil Chek analysis, data
available from NFPA, and various MSDS publications and may not accurately represent
all samples. ** When adjusting oil pressure refer to instructions found on page 26.
Adjusting the Temperature Controller
Two temperature settings control the preheat function; OUT1 maintains the temperature
within 5 degrees of the set point, and OUT2 prevents the burner from firing with oil that is
not yet at the set point temperature ( also know as interlock). There are two basic factory
set points based on the type of oil specified to be used as fuel.
SP1 SP2
Petroleum based oils 150
o
F 110
o
F
Vegetable based oils 170
o
F 120
o
F
When making adjustments follow this procedure:
1. Press and release the SET button. The current value of OUT1 is displayed and the
SP1 and the LED for the OUT1 lights blink. Press UP or DOWN to increase or
decrease the value. The range of OUT1 temperature is 120
o
F to 180
o
F. Press SET
to confirm the new value. This will then cause SP2 and the LED for OUT2 lights to
blink.

Table of Contents