Figure 13: Example of label to check PWR-XXXX part number
If you cannot read the base part number, ensure that the pull handles are both in a horizontal orientation
and that the sheet metal on the power cord face for each supply has the same perforation shapes.
When you add or replace a power supply unit in your system, be sure to verify the supply's features and
that the PWR-XXXX part numbers match to ensure that you have the correct supply.
Guidelines for AC-powered equipment
An AC-powered installation must meet these requirements:
Use a 15 amp external branch circuit protection device to install the unit.
Use one power feed for each individual power supply.
Important: The platform must be installed in a RESTRICTED ACCESS LOCATION, such as a central
office or customer premises environment.
Note: The power cables included with this unit ar
e for exclusive use with this unit and should not be used
with other electrical appliances.
Note: These guidelines apply to ST
ATIONARY PLUGGABLE EQUIPMENT TYPE A with simultaneous
multiple connections to the AC MAINS SUPPLY:
The building installation shall provide a means for connection to protective earth; and
The equipment is to be connected to that means; and
A SERVICE PERSON shall check whether or not the socket-outlet from which the equipment is to be
powered provides a connection to the building protective earth. If not, the SERVICE PERSON shall
arrange for the installation of a PROTECTIVE EARTHING CONDUCTOR from the separate
protective earthing terminal to the protective earth wire in the building.
Caution: High leakage curr
ent. Earth connection essential before connecting supply.