4 Planning and installation – Connections
27
Location of the chimney in the roof
The opening of the chimney must be at least 0.5m above the
highest edge of roofs with a slope of more than 20° or at least
1.0 m higher than roof surfaces which slope at 20° or less.
The effective height of a chimney is measured from the flue
entrance into it to the end of the chimney.
C
ONNECTING THE BOILER TO
THE CHIMNEY
The firing system must be connected with a connecting piece which
is as short as possible, at an angle which is less than 30 - 45° to the
chimney. You should aim for a connecting piece with a maximum
length of 1 m using just one fitting.
Every additional fitting results in a greater pressure loss in the
exhaust path and should thus be avoided. The same is true for overly
long connecting pieces. If, for constructional reasons, these must be
longer than 1 m, they should be adequately insulated (at least 5 cm
of mineral wool or equivalent material) and, if possible, fitted with an
upward inclination.
The following should also be considered:
The connecting piece may not protrude into the chimney.
If the system flue gas pipe has a larger diameter than the chimney,
the connecting piece must reduce its diameter to that of the
connection. In this case, the connecting piece should taper as
gently as possible.
Use bends rather than elbows; the radius of the elbow may not be
less than the diameter of the pipe.
The chimney should be vertical and straight, if possible without
deformations (take particular care in older buildings).
All of the cleaning doors and measurement hatches on the
chimney must have tight seals.
To reduce the entry of additional cold air, only attach one heat
generator per chimney.
To prevent dust from escaping, the flue pipe must be sealed with
heat-resistant silicone.
1 Auxiliary air unit
2Cleaning door
A) Chimney approx. 30° - 45°
B) Clearance at least 50 cm
Figure 4/3 - Chimney connection
2
A
B
1