Table 1 Performance Data
Boiler F80 F120 F160 F200 F240 F280
Boiler output Max kW 77.9 116.9 155.8 195.4 234.5 273.6
(non-condensing) Btu/h 265,800 398,900 531,600 666,700 800,100 933,500
Mean 70
o
C Min kW 23.3 23.3 29.1 43.1 47.0 51.0
Btu/h 79,500 79,500 99,300 147,050 160,350 174,000
Boiler output Max kW 82.2 123.4 164.5 207.8 249.4 290.9
(condensing) Btu/h 280,450 421,050 561,250 709,000 850,950 992,550
Mean 40
o
C Min kW 25.8 25.8 32.3 47.3 51.6 55.9
Btu/h 88,000 88,000 110,200 161,400 176,050 190,750
Boiler Input Net kW 80 120 160 200 240 280
Max Rate Btu/h 272,950 409,450 545,900 682,400 818,900 955,350
Gross kW 88.8 133.3 177.7 222.1 266.5 310.9
Btu/h 303,000 454,800 606,300 757,800 909,300 1,060,800
Boiler Input Net kW 24 24 30 44 48 52
Min Rate Btu/h 81,900 81,900 102,350 150,150 163,800 177,400
Gross kW 26.6 26.6 33.3 48.9 53.3 57.7
Btu/h 90,750 90,750 113,600 166,850 181,850 196,850
Maximum Gas Rate m
3
/h 8.1 12.1 16.1 20.1 24.2 28.2
ft
3
/h 286 427 569 710 855 996
Approx. flue gas @ max. rate m
3
/h 121 182 242 302 363 423
volume (@80
o
C) i.e. non-condensing ft
3
/h 4,270 6,410 8,550 10,690 12,820 14,960
Max. Flue Resistance Pa 100 100 150 150 150 150
Flue Gas CO
2
@ Max Rate % 9.3/9.8 9.3/9.8 9.3/9.8 9.3/9.8 9.3/9.8 9.3/9.8
G20/LNG @ Min. Rate % 9.1/9.6 9.1/9.6 9.1/9.6 9.1/9.6 9.1/9.6 9.1/9.6
NOx with O
2
= 0% mg/kWh 26 26 35 26 26 26
ppm 15 15 20 15 15 15
Seasonal Boiler Efficiency (Building Regs L2) 95.1 95.1 95.1 95.2 95.2 95.2
Note.
Natural gas consumption is calculated using a calorific value of
37.8MJ/m
3
(1038Btu/ft
3
) gross or 34 MJ/m
3
(910 Btu/ft
3
) nett at
15
o
C and 1013.25 mbar.
a. For l/s divide the gross heat input (kW) by the gross C.V. of
the gas (MJ/m
3
)
b. For ft/h
3
divide the gross heat input (Btu/h) by the gross C.V.
of the gas (Btu/ft
3
).
HEALTH & SAFETY DOCUMENT NO. 635
The electricity at work regulations, 1989. The manufacturer's
notes must NOT be taken, in any way, as overriding statutory
obligations.
IMPORTANT. These appliances are CE certified for safety and
performance. It is, therefore, important that no external control
devices, e.g. flue dampers, economisers etc., are directly
connected to these appliances unless covered by these
Installation and Servicing Instructions or as otherwise
recommended by Ideal Stelrad Group in writing. If in doubt
please enquire.
Any direct connection of a control device not approved by Ideal
Stelrad Group could invalidate the certification and the normal
appliance warranty. It could also infringe the Gas Safety
Regulations and the above regulations.
* Electricity supply and Fuse rating for pumps etc. refer to manufacturer's instructions.
Table 2 General Data
Boiler F80 F120 F160 F200 F240 F280
Gas supply 2H - G20 - 20mbar
Gas supply connection R (in. BSP) 1 1 1 1 1 1
Flow connection R (in. BSP) 2 2 2 2 2 2
Return connection R (in. BSP) 2 2 2 2 2 2
Hydraulic Resistance @ 20
o
C mbar 80 85 90 95 100 105
Max Press (sealed system) bar (psi) 6 (87) 6 (87) 6 (87) 6 (87) 6 (87) 6 (87)
Maximum Static Head m (ft) 61 (200) 61 (200) 61 (200) 61 (200) 61 (200) 61 (200)
Boiler Electricity Supply 230V - 50Hz
Boiler Fuse Rating External: 3A* Internal: 2AT, 4AT External: 5A* Internal: 2AT, 4AT
Power Consumption (boiler only) W 250 250 400 400 400 400
Air Inlet O/D m m 110 110 110 110 110 110
Flue Size dia m m 150 150 150 200 200 200
Condensate drain m m 21.5 21.5 21.5 21.5 21.5 21.5
Boiler dry weight (unpacked) kg (lb) 132 (291) 150 (331) 168 (370) 198 (437) 215 (474) 233 (514)
Water Content l (gal) 11.0 (2.4) 14.3 (3.2) 17.5 (3.9) 18.4 (4.1) 24.0 (5.3) 27.2 (6.0)