Page #41 background imageLoading...
Page #41 background image
FERROLI F30
41
Chart 6
Check ignition system
Is LED1 light on?
Does sparking start
at burner?
Does burner light?
YES
Is LED2 on
after 10 seconds?
NO
YES
Go to chart 5
Reset lockout
YES
Does burner light now?
Is flame present before
lockout condition?
NO
YES
NO
Check and if necessary
replace safety thermostat
Check electrodes and
leads for damage
and correct connection
Check and if necessary
replace P.C.B.
Adjust with P4 ignition
burner pressure
Check and if necessary
clean burner
Check and if necessary
clean injectors
Check and if necessary
clean flame electrode
Check right position
of spark electrode
Check wires
Check gas supply
is live and purged
Check and if necessary
replace gas valve
NO
YES
Check and if necessary
replace P.C.B.
NO
Is LED2 on
without
the boiler sparking
YES NO
Re-check
air pressure switch

Table of Contents

Other manuals for Ferroli F30

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the Ferroli F30 and is the answer not in the manual?

Ferroli F30 Specifications

General IconGeneral
Max. Heat Output (kW)30
ModulationYes
IgnitionElectronic
Safety featuresOverheat protection, Flame failure device, Frost protection
Fuel TypeNatural Gas

Related product manuals