Connections
NOTE
To prevent interference, unscreened communic-
ation and/or sensor cables to external connec-
tions must not be laid closer than 20 cm from
high voltage cables.
Power connection
F470 must be installed via an isolator switch with a
minimum breaking gap of 3mm. Minimum cable area
must be sized according to the fuse rating used. Supplied
cable (length approx. 2 m) for incoming supply electricity
is connected to terminal block X1 on the immersion
heater board (AA1). The connection cable can be found
on the back of F470 (see dimensions diagram below).
50
300
30
1670
Power supply cable
UB1 and UB2
NOTE
F470 is not switchable between 3x230V and
3x400V.
Connection 3x400V
AA1-X1
PE1
L1 1 L2 L3PE0N
AA1-X1
Connection 3x230V
PE1
1 L2 2 L3L1PE
AA1-X1
AA1-X1
If separate supply to the compressor and immersion
heater is required, see section "Possible selection for AUX
inputs" on page 29.
Tariff control
If the voltage to the immersion heater and/or the com-
pressor disappears for a certain period, there must also
be blocking via the AUX-input at the same time, see
"Possible selection for AUX inputs".
23Chapter 5 | Electrical connectionsNIBE F470

Other manuals for Nibe F470

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the Nibe F470 and is the answer not in the manual?

Nibe F470 Specifications

General IconGeneral
TypeExhaust air heat pump
ERP class heatingA++
Energy Efficiency ClassA++
Integrated Hot Water Tank180 liters
RefrigerantR290
ApplicationResidential

Related product manuals