Settings
BT30
AA1-X3
AA1-SF2
AA1-X7
Electrical addition - maximum output
The immersion heater output is divided into steps, ac-
cording to the table.
Setting maximum output in the electric additional heat
is done in menu 5.1.12.
When switching from 3x400 V to 1x230 V, the immersion
heater is limited to 2 kW. Min. fuse rating 16 A.
Power steps of the immersion heater
3x400V copper
Max (A) L3Max (A) L2Max (A) L1Electrical
addition
(kW)
--6.30.0
8.7-6.32.0
8.77.36.33.7
11.68.46.34.6*
11.67.317.97.0
20.38.417.99.3
*Factory setting
The table displays the maximum phase current for the
relevant power step for the heat pump.
If the current sensors are connected, the heat pump
monitors the phase currents and allocates the electrical
steps automatically to the least loaded phase.
3x400V stainless steel
Max (A) L3Max (A) L2Max (A) L1Electrical
addition
(kW)
--6.30.0
8.7-6.32.0
8.711.66.34.7
11.611.66.35.6*
11.611.617.98.0
20.312.717.910.3
*Factory setting
The table displays the maximum phase current for the
relevant power step for the heat pump.
If the current sensors are connected, the heat pump
monitors the phase currents and allocates the electrical
steps automatically to the least loaded phase.
3x230V
Max (A) L3Max (A) L2Max (A) L1Electrical
addition
(kW)
-4.54.50.0
8.711.64.52.0
17.611.614.44.7
25.320.014.46.7*
20.124.124.18.0
28.031.624.110.0
*Factory setting
The table displays the maximum phase current for the
relevant power step for the heat pump.
If the current sensors are connected, the heat pump
monitors the phase currents and allocates the electrical
steps automatically to the least loaded phase.
Output locking
F470 follows applicable building regulations (BBR). This
means that the maximum power output (maximum in-
stalled electrical output for heating) can be locked in
menu 5.1.13. To then change the maximum power out-
put, parts of the product must be replaced.
Emergency mode
When the heat pump is set to emergency mode (SF1 is
set to ), only the most necessary functions are activ-
ated.
The compressor and fans are off and heating is man-
aged by the immersion heater.
The load monitor is not connected.
NIBE F470Chapter 5 | Electrical connections26

Other manuals for Nibe F470

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the Nibe F470 and is the answer not in the manual?

Nibe F470 Specifications

General IconGeneral
TypeExhaust air heat pump
ERP class heatingA++
Energy Efficiency ClassA++
Integrated Hot Water Tank180 liters
RefrigerantR290
ApplicationResidential

Related product manuals