Menu 5.1.1 - hot water settings
economy
Setting range start temp. economy: 15 - 52 °C
Factory setting start temp. economy: 45 °C
F470 copper: 43 °C
F470 stainless steel: 42 °C
Setting range stop temp. economy: 15 - 55 °C
Factory setting stop temp. economy: 51 °C
F470 copper: 47 °C
F470 stainless steel: 46 °C
normal
Setting range start temp. normal: 15 - 52 °C
Factory setting start temp. normal: 49 °C
F470 copper: 47 °C
F470 stainless steel: 46 °C
Setting range stop temp. normal: 15 - 55 °C
Factory setting stop temp. normal: 55 °C
F470 copper: 51 °C
F470 stainless steel: 50 °C
luxury
Setting range start temp. lux: 15 - 62 °C
Factory setting start temp. lux: 52 °C
F470 copper: 50 °C
F470 stainless steel: 49 °C
Setting range stop temp. lux: 15 - 65 °C
Factory setting stop temp. lux: 58 °C
F470 copper: 54 °C
F470 stainless steel: 53 °C
stop temp. per. increase
Setting range: 55 – 70 °C
Factory setting: 60 °C
Here you set the start and stop temperature of the hot
water for the different comfort options in menu 2.2 as
well as the stop temperature for periodic increase in
menu 2.9.1.
Menu 5.1.2 - max flow line temperature
climate system
Setting range: 20-70 °C
Default value: 60 °C
Set the maximum supply temperature for the climate
system here. If the installation has more than one climate
system, individual maximum supply temperatures can
be set for each system. Climate systems 2 - 8 cannot be
set to a higher max supply temperature than climate
system 1.
Caution
Underfloor heating systems are normally max
flow line temperature set between 35 and 45
°C.
Check the max floor temperature with your floor
supplier.
Menu 5.1.4 - alarm actions
Select if you want the heat pump to alert you that there
is an alarm in the display here.
Caution
If no alarm action is selected, it can result in
higher energy consumption in the event of an
alarm.
Menu 5.1.5 - fan sp. exhaust air
normal and speed 1-4
Setting range: 0 – 100 %
Set the speed for the five different selectable speeds for
the fan here.
Caution
An incorrectly set ventilation flow can damage
the house and may also increase energy con-
sumption.
Menu 5.1.6 - fan sp. supply air
normal and speed 1-4
Setting range: 0 – 100 %
Set the speed for the five different selectable speeds for
the fan here.
Caution
An incorrectly set value may damage the house
in the long term and possibly increase energy
consumption.
NIBE F470Chapter 8 | Control - Menus46