F600 Step By Step Guide 18
The drive must be connected to the system ground of the AC supply. The ground wiring must
conform to local regulations and codes of practice.
Table 6-3 Protective ground cable ratings
Electrochemical corrosion of grounding terminals
Ensure that grounding terminals are protected against corrosion i.e. as could be caused
by condensation.
The ground loop impedance must conform to the requirements of local safety regulations.
The drive must be grounded by a connection capable of carrying the prospective fault
current until the protective device (fuse, etc.) disconnects the AC supply.
The ground connections must be inspected and tested at appropriate intervals.
Input phase conductor size Minimum ground conductor size
10 mm²
Either 10 mm² or two conductors of the same cross-sectional area as the
input phase conductor
> 10 mm² and 16 mm² The same cross-sectional area as the input phase conductor
> 16 mm² and 35 mm² 16 mm²
> 35 mm² Half of the cross-sectional area of the input phase conductor