Basic Programming 5 - 24
If L3-04=2, the intelligent stall prevention function is enabled. The active deceleration time is used as a starting point and the
Drive will attempt to decelerate as quickly as possible without causing the DC Bus voltage to exceed the stall prevention level.
The fastest time possible is 1/10 the active deceleration time.
If L3-04=3, the stall prevention with braking resistor function is enabled. The DC bus voltage level is controlled during fast
deceleration and allows for a faster than normal deceleration time. Use this setting with a braking resistor when overvoltage
fault (OV) sometimes occurs even under settings 1 or 2.
IMPORTANT
In Flux Vector Control Mode (A1-02=3), setting stall prevention with DB resistor (L3-04=3) cannot be done.
http://www.aotewell.com
Aotewell
Email: Sales@aotewell.com
Tel: +(86) 755 8660 6182
Aotewell
http://www.aotewell.com

Table of Contents

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC

Related product manuals