Electrical Installation 2 - 34
PG-B2
The terminal specifications for the PG-B2 are given in Table 2.19.
Wiring the PG-B2
Wiring examples are provided in Fig 2.19 and Fig. 2.20 for the PG-B2.
Fig 2.19 PG-B2 Open-Collector Input Wiring - Sourcing PG
Table 2.19 PG-B2 Terminal Specifications
Terminal No. Contents Specifications
TA1
1
Power supply for pulse generator
12Vdc (±5%), 200mA max.
2 0Vdc (GND for power supply)
3
A-phase pulse input terminals
H: +8 to 12Vdc
L: +1Vdc max.
(Maximum response frequency: 30 kHz)
4 Pulse input common
5
B-phase pulse input terminals
H: +8 to 12Vdc
L: +1Vdc max.
(Maximum response frequency: 30 kHz)
6 Pulse input common
TA2
1
A-phase monitor output terminals
Open collector output, 24Vdc, 30mA max.
2 A-phase monitor output common
3
B-phase monitor output terminals
Open collector output, 24Vdc, 30mA max.
4 B-phase monitor output common
TA3 (E) Shield connection terminal -
Drive
Power supply +12Vdc
Power supply 0Vdc
A-phase pulse input (+)
A-phase pulse input (–)
B-phase pulse input (+)
B-phase pulse input (–)
A-phase pulse monitor output
B-phase pulse monitor output
4CN
R/L1
S/L2
T/L3
Branch
Circuit
Protection
•Shielded twisted-pair wires must be used for signal lines.
•Do not use the PG-B2's power supply for anything other than the pulse generator (encoder).
Using it for another purpose can cause malfunctions due to noise.
•The length of the pulse generator's wiring must not be more than 100 meters.
•The direction of rotation of the PG can be set in parameter F1-05 (PG Rotation).
The factory preset is for forward rotation, A-phase advancement.