Start-Up 4 - 12
Quick Setting Parameters
The following Drive parameters located in the Quick Setting menu need to be set according to the application. Refer to
Chapter 5 Basic Programming section for more details on each parameter.
Note: Not all parameters are available for all Control Methods. See Control Method column.
Parameter
No.
Parameter Name
Digital Operator Display
Description
Setting
Range
Factory
Setting
Control Method
V/F
V/F
w/
PG
OLV FV
A1-02
Control Method Selection
Control Method
Selects the Control Method of the Drive.
0: V/F control without PG
1: V/F control with PG
2: Open Loop Vector
3: Flux Vector (Closed Loop Vector)
0 to 3 0 Q Q Q Q
b1-01
Frequency Reference
Selection
Reference Source
Selects the frequency reference input source.
0: Operator - Digital preset speed U1-01 or d1-01 to d1-17.
1: Terminals - Analog Input Terminal A1 (Terminal A2 sums
together with terminal A1 when H3-09=0)
2: Serial Com - Modbus RS-422/485 terminals R+, R-, S+ and S-
3: Option PCB - Option board connected on 2CN
4: Pulse Input
0 to 4 1 Q Q Q Q
b1-02
Run Command Selection
Run Source
Selects the run command input source.
0: Operator - RUN and STOP keys on Digital Operator
1: Terminals - Contact closure on terminals S1 or S2
2: Serial Com - Modbus RS-422/485 terminals R+, R-, S+ and S-
3: Option PCB - Option board connected on 2CN
0 to 3 1 Q Q Q Q
b1-03
Stopping Method Selection
Stopping Method
Selects the stopping method when the run command is removed.
0: Ramp to Stop
1: Coast to Stop
2: DC Injection to Stop
3: Coast with Timer (A new run command is ignored if input
before the timer expires.)
0 to 3 0 Q Q Q Q
C1-01
Acceleration Time 1
Accel Time 1
Sets the time to accelerate from zero to maximum frequency
(E1-04).
0.0
to
6000.0
10.0sec
QQ Q Q
C1-02
Deceleration Time 1
Decel Time 1
Sets the time to decelerate from maximum frequency to zero
(E1-04).
QQ Q Q
C6-02
Carrier Frequency Selection
CarrierFreq Sel
Selects the number of pulses per second of the output voltage
waveform. Setting range determined by C6-01 setting.
0: Low noise
1: Fc = 2.0 kHz
2: Fc = 5.0 kHz
3: Fc = 8.0 kHz
4: Fc = 10.0 kHz
5: Fc = 12.5 kHz
6: Fc = 15.0 kHz
F: Program (Determined by the settings of C6-03 thru C6-05)
Va ri es
by
kVA
Va ri es
by
kVA
QQ Q Q
d1-01
Frequency Reference 1
Reference 1
Setting units are affected by o1-03.
0.00
to
E1-04
Va lu e
0.00Hz Q Q Q Q
d1-02
Frequency Reference 2
Reference 2
Frequency reference when multi-function input “Multi-step speed
reference 1” is ON. Setting units are affected by o1-03.
0.00Hz Q Q Q Q
d1-03
Fr
equency Reference 3
Reference 3
Frequency reference when multi-function input “Multi-step speed
reference 2” is ON. Setting units are affected by o1-03.
0.00Hz Q Q Q Q
d1-04
Frequency Reference 4
Reference 4
Frequency reference when multi-function input “Multi-step speed
reference 1,2” is ON. Setting units are affected by o1-03.
0.00Hz Q Q Q Q
d1-17
Jog Frequency Reference
Jog Reference
Frequency reference when:
“Jog Frequency Reference”, “Forward Jog”, or “Reverse Jog” is
selected via multi-function input terminals or JOG key is pressed
on the operator keypad. Jog reference has priority over frequency
reference 1 to 4. Setting units are affected by o1-03.
6.00Hz Q Q Q Q
Denotes that parameter can be changed when the Drive is running.
http://www.aotewell.com
Aotewell
Email: Sales@aotewell.com
Tel: +(86) 755 8660 6182
Aotewell
http://www.aotewell.com

Table of Contents

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC