Specifications C - 3
480Vac
Table C.2 480Vac Drive Specifications
Model Number CIMR-F7U 40P4 40P7 41P5 42P2 43P7 44P0 45P5 47P5 4011 4015 4018 4022
Rated output
capacity
(kVA)
1.4 1.6 2.8 4.0 5.8 6.6 9.5 13.0 18.0 24.0 30.0 34.0
Horsepower
*2
0.5/0.751235-7.51015202530
Rated output current
(A)
1.8 2.1 3.7 5.3 7.6 8.7 12.5 17.0 24.0 31.0 39.0 45.0
Overload capacity
*3
(% of rated output
current for 60 sec)
150
Current limit (% of
rated output current)
150
Carrier frequency
*4
2kHz
Maximum output
frequency
300.0Hz
Rated output
capacity (kVA)
1.4 1.6 2.8 4.0 5.8 6.6 9.5 13.0 21.0 26.0 30.0 38.0
Horsepower
*2
0.5/0.751235-7.51015/202530-
Rated output current
(A)
1.8 2.1 3.7 5.3 7.6 8.7 12.5 17.0 27.0 34.0 40.0 50.4
Overload capacity
*3
(% of rated output
current for 60 sec)
120 120 120 120 120 120 120 120 107 109 117 107
Current limit
(
% of rated
output current)
120
Carrier frequency (kHz)
*5
15 15 15 15 15 15 15 15 8 10 10 10
Maximum output
frequency
400.0Hz
Maximum output voltage 3-phase; 380, 400, 415, 440, 460, or 480Vac (Proportional to input voltage.)
Rated voltage
Rated frequency
3-phase, 380, 400, 415, 440, 460 or 480Vac, 50/60Hz
Rated input current -
Heavy Duty
*1
(A)
2.2 2.5 4.4 6.4 9.0 10.4 15 20 29 37 47 50
Rated input current -
Normal Duty
*1
(A)
2.2 2.5 4.4 6.4 9.0 10.4 15 20 33 40 48 55
Allowable voltage
fluctuation
+ 10%, - 15%
Allowable frequency
fluctuation
±5%
Measures
for power
supply
harmonics
DC Reactor Optional
12-pulse
Rectification
Not possible
*1 The difference between Heavy Duty ratings and the Normal Duty ratings for the Drive are the rated input and output current, overload capacity, carrier frequency, current limit,
and maximum output frequency. Parameter C6-01 must be set to value of “0” for Heavy Duty ratings and “2” for Normal Duty ratings. Factory default is Heavy Duty (C6-01=0).
*2 Horsepower ratings are based on 230V or 460V NEC Table 430.150. The maximum applicable motor output is given for a standard 4-pole motor. When selecting the actual
motor and Drive, be sure that the Drive's rated output current is appropriate for the motor's rated current.
*3 Model 2110 has an overload rating of 138% of rated output current for 60 seconds and a current limit rating of 138%. Models 4220 and 4300 have an overload rating of 150%
of rated output current for 45 seconds and a current limit rating of 150%.
*4 When setting the carrier frequency above the factory default, the Drive must be derated.
*5 Heavy Duty ratings for models 2110, 4220 and 4300 are effective in software version VSF103021 and higher.
*6 Each value shown is the Maximum carrier frequency and default carrier frequency.
*7 The carrier frequency for Heavy Duty is default to 2 kHz. Software version VSF103021 and higher may allow the carrier frequency to be increased above 2 kHz with a
reduction in continuous rated output current. Refer to C6-02 in Chapter 5 for further details.
O
utput rat
i
ngs
Heavy Duty
*1
Normal Duty
*1
Power supp
l
y c
h
aracter
i
st
i
cs
Control characteristics
http://www.aotewell.com
Aotewell
Email: Sales@aotewell.com
Tel: +(86) 755 8660 6182
Aotewell
http://www.aotewell.com

Table of Contents

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC