EasyManuals Logo

YASKAWA F7 User Manual

YASKAWA F7
255 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Page #98 background imageLoading...
Page #98 background image
Start-Up 4 - 13
Parameter
No.
Parameter Name
Digital Operator Display
Description
Setting
Range
Factory
Setting
Control Method
V/F
V/F
w/
PG
OLV FV
E1-01
Input Voltage Setting
Input Voltage
Set to the nominal voltage of the incoming line, sets maximum/
base voltage used by preset V/F patterns (E1-03 = 0 to E), adjusts
the levels of Drive protective features (i.e. Overvoltage, braking
resistor turn-on, stall prevention, etc.).
155 to
255.0
(240V)
310 to
510.0
(480V)
240V
480V
QQ Q Q
E1-03
V/F Pattern Selection
V/F Selection
Set to the type of motor being used and the type of application.
The Drive operates utilizing a set V/F pattern to determine the
appropriate output voltage level for each commanded speed. There
are 15 different preset V/F patterns to select from (E1-03 = 0 to E)
with varying voltage profiles, base levels (base level = frequency
at which maximum voltage is reached), and maximum frequencies.
There are also settings for Custom V/F patterns that will use the
settings of parameters E1-04 through E1-13. E1-03 = F selects a
custom V/F pattern with an upper voltage limit and E1-03 = FF selects
a custom V/F pattern without an upper voltage limit.
0: 50Hz
1: 60Hz
2: 60Hz (50Hz Base)
3: 72Hz (60Hz Base)
4: 50Hz VT1
5: 50Hz VT2
6: 60Hz VT1
7: 60Hz VT2
8: 50Hz HST1
9: 50Hz HST2
A: 60Hz HST1
B: 60Hz HST2
C: 90Hz (60Hz Base)
D: 120Hz (60Hz Base)
E: 180Hz (60Hz Base)
F: Custom V/F
FF:Custom w/o limit
0 to FF F Q Q - -
E1-04
Maximum Output Frequency
Max Frequency
These parameters are only applicable when V/F Pattern Selection
is set to Custom (E1-03 = F or FF). To set V/F characteristics in a
straight line, set the same values for E1-07 and E1-09. In this case,
the setting for E1-08 will be disregarded. Always ensure that the
four frequencies are set in the following manner:
E1-04 E1-12 E1-06 > E1-07 E1-09
E2-04 is automatically set during Auto-Tuning.
HD: 40.0
to 300.0
ND2: 40.0
to 400.0
60.0Hz Q Q Q Q
E1-05
Maximum Output Voltage
Max Voltage
0 to 255.0
(240V)
0 to 510.0
(480V)
240V
480V
QQ Q Q
E1-06
Base Frequency
Base Frequency
0.0 to
200.0
60.0Hz Q Q Q Q
E1-09
Minimum Output Frequency
Min Frequency
0.0 to
200.0
1.5Hz Q Q Q A
E1-13
Base Voltage
B
ase Voltage
0 to 255.0
(240V)
0 to 510.0
(480V)
0.0VAC A A Q Q
E2-01
Motor Rated Current
Motor Rated FLA
Varies by
kVA
Varies by
kVA
QQ Q Q
E2-04
Number of Motor Poles
Number of Poles
2 to 48 4 - Q - Q
E2-11
Motor Rated Output
Motor Rated Power
Set to the motor rated power in KW.
This value is automatically set during Auto-Tuning.
0.00 to
650.00
Varies by
kVA
QQ Q Q
F1-01
PG Parameter
PG Pulse/Rev
Sets the number of pulses per revolution of the encoder (pulse
generator). This value is automatically set during Auto-Tuning.
0 to 60000 1024 - Q - Q
Denotes that parameter can be changed when the Drive is running.
Output voltage (V)
Frequency (Hz)
E1-09 E1-07 E1-06 E1-11 E1-04
E1-05
E1-12
E1-13
E1-08
E1-10
http://www.aotewell.com
Aotewell
Email: Sales@aotewell.com
Tel: +(86) 755 8660 6182
Aotewell
http://www.aotewell.com

Table of Contents

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC

Related product manuals