EasyManuals Logo

YASKAWA F7 User Manual

YASKAWA F7
255 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Page #172 background imageLoading...
Page #172 background image
Parameters A - 7
PID Control
b5-01
PID Function Setting
PID Mode
This parameter determines the function of the PID control.
0: Disabled
1: D = Feedback
2: D = Feed-Forward
3: Freq. Ref. + PID output (D = Feedback)
4: Freq. Ref. + PID output (D = Feed-Forward)
0 to 4 0 A A A A
b5-02
Proportional Gain Setting
PID Gain
Sets the proportional gain of the PID controller.
0.00 to
25.00
1.00 A A A A
b5-03
Intregral Time Setting
PID I Time
Sets the integral time for the PID controller. A setting of zero
disables integral control.
0.0 to
360.0
1.0sec A A A A
b5-04
Intregral Limit Setting
PID I Limit
Sets the maximum output possible from the integrator. Set as a
percentage (%) of maximum frequency.
0.0 to
100.0
100.0% A A A A
b5-05
Derivative Time
PID D Time
Sets D control derivative time. A setting of 0.00 disables derivative
control.
0.00 to
10.00
0.00sec A A A A
b5-06
PID Output Limit
PID Limit
Sets the maximum output possible from the entire PID controller.
Set as a percentage (%) of maximum frequency.
0.00 to
100.0
100.0% A A A A
b5-07
PID Offset Adjustment
PID Offset
Sets the amount of offset of the output of the PID controller. Set as a
percentage (%) of maximum frequency.
The offset is summed with the PID output. This can be used to
artificially kick-start a slow starting PID loop.
–100.0 to
+100.0
0.0% A A A A
b5-08
PID Primary Delay Time
Constant
PID Delay Time
Sets the amount of time for the filter on the output of the PID
controller.
0.00 to
10.00
0.00sec A A A A
b5-09
PID Output Level
Selection
Output Level Sel
Determines whether the PID controller will be direct or reverse
acting.
0: Normal Output
1: Reverse Output
0 to 1 0 A A A A
b5-10
PID Output Gain Setting
Output Gain
Sets the output gain of the PID controller.
0.0 to
25.0
1.0 A A A A
b5-11
PID Output Reverse
Selection
Output Rev Sel
0: 0 limit (when PID output goes negative, Drive stops). 0 limit is
automatic when reverse prohibit is selected using b1-04.
1: Reverse (when PID goes negative, Drive reverses).
0 to 1 0 A A A A
b5-12
PI
D Feedback Reference
Missing Detection
Selection
Fb los Det Sel
0: Disabled
1: Alarm
2: Fault
0 to 2 0 A A A A
b5-13
PID Feedback Loss
Detection Level
Fb los Det Lvl
Sets the PID feedback loss detection level as a percentage (%) of
maximum frequency (E1-04).
0 to 100 0% A A A A
b5-14
PID Feedback Loss
Detection Time
Fb los Det Time
Sets the PID feedback loss detection delay time in terms of
seconds.
0.0 to
25.5
1.0sec A A A A
b5-15
PID Sleep Function Start
Level
PID Sleep Level
Sets the sleep function start frequency.
Va ri es
by
Duty
Rating*
0.0Hz A A A A
b5-16
PID Sleep Delay Time
PID Sleep Time
Sets the sleep function delay time in terms of seconds.
0.0 to
25.5
0.0sec A A A A
b5-17
PID Accel/Decel Time
PID Acc/Dec Time
Applies an accel/decel time to the PID setpoint reference. The
Drive’s standard softstarter (C1-XX and S-curve) still affects the
output of the PID algorithm.
0.0 to
25.5
0.0sec A A A A
b5-18
PID Setpoint Selection
PID Setpoint Sel
Allows the b5-19 setting to be the PID target setpoint value.
0: Disabled
1: Enabled
0 to 1 0 A A A A
b5-19
PID Setpoint Value
PID Setpoint
Sets the PID target value. Use only when b5-18 = 1
0.0 to
100.0
0.0% A A A A
Denotes that parameter can be changed when the Drive is running.
* For Heavy Duty (HD) Rating (C6-01=0): Setting Range=0.0 to 300.0. For Normal Duty (ND) Rating (C6-01=2): Setting Range=0.0 to 400.0.
Table A.1 F7 Parameter List (Continued)
Parameter
No.
Parameter Name
Digital Operator Display
Description
Setting
Range
Factory
Setting
Control Method
V/F
V/F
w/PG
Open
Loop
Vector
Flux
Vector
http://www.aotewell.com
Aotewell
Email: Sales@aotewell.com
Tel: +(86) 755 8660 6182
Aotewell
http://www.aotewell.com

Table of Contents

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC

Related product manuals