Parameters A - 29
H4-02
Terminal FM Gain Setting
Terminal FM Gain
Sets terminal FM output level when selected monitor is at 100%.
0.0 to
1000.0
100.0% Q Q Q Q
H4-03
Terminal FM Bias Setting
Terminal FM Bias
Sets terminal FM output level when selected monitor is at 0%.
–110.0 to
110.0
0.0% A A A A
H4-04
Terminal AM Monitor
Selection
Terminal AM Sel
Selects which monitor will be the output on terminals AM and FC.
Same function choices as H4-01.
1 to 45 3 A A A A
H4-05
Terminal AM Gain Setting
Terminal AM Gain
Sets terminal AM output voltage (in percent of 10Vdc) when
selected monitor is at 100% output.
0.0 to
1000.0
50.0% Q Q Q Q
H4-06
Terminal AM Bias Setting
Terminal AM Bias
Sets terminal AM output voltage (in percent of 10Vdc) when
selected monitor is at 0% output.
–110.0 to
110.0
0.0% A A A A
H4-07
Terminal FM Signal Level
Selection
FM Level Select 1
Selects the signal level of terminal FM.
0: 0 to 10Vdc
1: -10 to +10Vdc
2: 4 to 20mA*
0 or 2 0 A A A A
H4-08
Terminal AM Signal Level
Selection
AM Level Select 2
Selects the signal level of terminal AM.
0: 0 to 10Vdc
1: -10 to +10Vdc
2: 4 to 20mA*
0 or 2 0 A A A A
Serial Communications Setup
H5-01
Drive Node Address
Serial Comm Adr
Selects Drive station node number (address) for Modbus terminals
R+, R-, S+, S-. The Drive’s power must be cycled for the setting to
take effect.
0 to 20
Hex
1F A A A A
H5-02
Communication Speed
Selection
Serial Baud Rate
Selects the baud rate for Modbus terminals R+, R-, S+ and S-. The
Drive’s power must be cycled for the setting to take effect.
0: 1200 bps
1: 2400 bps
2: 4800 bps
3: 9600 bps
4: 19200 bps
0 to 4 3 A A A A
H5-03
Communication Parity
Selection
Serial Com Sel
Selects the communication parity for Modbus terminals R+, R-, S+
and S-. The Drive’s power must be cycled for the setting to take
effect.
0: No Parity
1: Even Parity
2: Odd Parity
0 to 2 0 A A A A
H5-04
Stopping Method After
Communication Error
Serial Fault Sel
Selects the stopping method when a communication timeout fault
(CE) is detected.
0: Ramp to Stop
1: Coast to Stop
2: Fast-Stop
3: Alarm Only
0 to 3 3 A A A A
H5-05
Communication Fault
Detection Selection
Serial Flt Dtct
Enables or disables the communications timeout fault (CE).
0: Disabled - A communication loss will not cause a
communication fault.
1: Enabled - If communication is lost for more than 2 seconds, a CE
fault will occur.
0 to 1 1 A A A A
H5-06
Drive Transmit Wait Time
Transmit WaitTIM
Set the delay time from when the Drive receives data to when the
Drive sends data.
5 to 65 5ms A A A A
H5-07
RTS Control Selection
RTS Control Sel
Enables or disables “request to send” (RTS) control:
0: Disabled - RTS is always on
1: Enabled - RTS turns on only when sending
0 to 1 1 A A A A
H5-10
<3021>
Unit Selection for
MEMOBUS Register 0025H
MEMOBUS 25H UNIT
Selects the units used for MEMOBUS registry 0025H (monitors the
output voltage reference).
0: 0.1 V units
1: 1 V units
0, 1 0 A A A A
Pulse I/O Setup
H6-01
Terminal RP Pulse Train Input
Function Selection
Pulse Input Sel
Selects the function of pulse train terminal RP.
0: Frequency reference
1: PID feedback value
2: PID setpoint value
0 to 2 0 A A A A
H6-02
Pulse Train Input Scaling
Pulse In Scaling
Sets the number of pulses (in Hz) that is equal to the maximum
output frequency E1-04.
1000 to
32000
1440Hz A A A A
H6-03
Pulse Train Input Gain
Pulse Input Gain
Sets the output level when the pulse train input is at 100% as a
percentage of maximum output frequency E1-04.
0.0 to
1000.0
100.0% A A A A
Denotes that parameter can be changed when the Drive is running.
Note: Some digital outputs are control method dependent.
Table A.1 F7 Parameter List (Continued)
Parameter
No.
Parameter Name
Digital Operator Display
Description
Setting
Range
Factory
Setting
Control Method
V/F
V/F
w/PG
Open
Loop
Vector
Flux
Vector