5-34 F35 Multiple Feeder Protection System GE Multilin
5.2 PRODUCT SETUP 5 SETTINGS
5
5.2.7 FAULT REPORTS
PATH: SETTINGS Ö PRODUCT SETUP ÖØ FAULT REPORTS Ö FAULT REPORT 1(5)
The F35 relay supports one fault report and an associated fault locator per CT bank to a maximum of 5. The signal source
and trigger condition, as well as the characteristics of the line or feeder, are entered in this menu.
The fault report stores data, in non-volatile memory, pertinent to an event when triggered. The captured data contained in
the FaultReport.txt file includes:
Fault report number
Name of the relay, programmed by the user
Firmware revision of the relay
Date and time of trigger
Name of trigger (specific operand)
Line/feeder ID via the name of a configured signal source
Active setting group at the time of trigger
Pre-fault current and voltage phasors (two cycles before either a 50DD disturbance associated with fault report source
or the trigger operate)
Fault current and voltage phasors (one cycle after the trigger)
Elements operated at the time of triggering
Events: 9 before trigger and 7 after trigger (only available via the relay webpage)
Fault duration times for each breaker (created by the breaker arcing current feature)
FAULT REPORT 1
FAULT REPORT 1
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
MESSAGE
FAULT REPORT 1 TRIG:
Off
Range: FlexLogic™ operand
MESSAGE
FAULT REPORT 1 Z1
MAG: 3.00 Ω
Range: 0.01 to 250.00 ohms in steps of 0.01
MESSAGE
FAULT REPORT 1 Z1
ANGLE: 75°
Range: 25 to 90° in steps of 1
MESSAGE
FAULT REPORT 1 Z0
MAG: 9.00 Ω
Range: 0.01 to 650.00 ohms in steps of 0.01
MESSAGE
FAULT REPORT 1 Z0
ANGLE: 75°
Range: 25 to 90° in steps of 1
MESSAGE
FAULT REPORT 1 LINE
LENGTH UNITS: km
Range: km, miles
MESSAGE
FAULT REP 1 LENGTH
(km ): 100.0
Range: 0.0 to 2000.0 in steps of 0.1
MESSAGE
FAULT REPORT 1 VT
SUBSTITUTION: None
Range: None, I0, V0
MESSAGE
FAULT REP 1 SYSTEM
Z0 MAG: 2.00 Ω
Range: 0.01 to 650.00 ohms in steps of 0.01
MESSAGE
FAULT REP 1 SYSTEM
Z0 ANGLE: 75°
Range: 25 to 90° in steps of 1