GE Multilin F35 Multiple Feeder Protection System 6-19
6 ACTUAL VALUES 6.3 METERING
6
6.3.4 FLEXELEMENTS™
PATH: ACTUAL VALUES ÖØ METERING ÖØ FLEXELEMENTS Ö FLEXELEMENT 1(16)
The operating signals for the FlexElements™ are displayed in pu values using the following definitions of the base units.
6.3.5 IEC 61580 GOOSE ANALOG VALUES
PATH: ACTUAL VALUES ÖØ METERING ÖØ IEC 61850 GOOSE ANALOGS
The F35 Multiple Feeder Protection System is provided with optional IEC 61850 communications capabil-
ity. This feature is specified as a software option at the time of ordering. Refer to the Ordering section of
chapter 2 for additional details. The IEC 61850 protocol features are not available if CPU type E is
ordered.
The IEC 61850 GGIO3 analog input data points are displayed in this menu. The GGIO3 analog data values are received
via IEC 61850 GOOSE messages sent from other devices.
FLEXELEMENT 1
FLEXELEMENT 1
OpSig: 0.000 pu
Table 6–2: FLEXELEMENT™ BASE UNITS
dcmA BASE = maximum value of the DCMA INPUT MAX setting for the two transducers configured
under the +IN and –IN inputs.
FREQUENCY f
BASE
= 1 Hz
PHASE ANGLE ϕ
BASE
= 360 degrees (see the UR angle referencing convention)
POWER FACTOR PF
BASE
= 1.00
RTDs BASE = 100°C
SOURCE CURRENT I
BASE
= maximum nominal primary RMS value of the +IN and –IN inputs
SOURCE ENERGY
(SRC X Positive and Negative
Watthours); (SRC X Positive and
Negative Varhours)
E
BASE
= 10000 MWh or MVAh, respectively
SOURCE POWER P
BASE
= maximum value of V
BASE
× I
BASE
for the +IN and –IN inputs
SOURCE THD & HARMONICS BASE = 1%
SOURCE VOLTAGE V
BASE
= maximum nominal primary RMS value of the +IN and –IN inputs
IEC 61850
GOOSE ANALOGS
ANALOG INPUT 1
0.000
MESSAGE
ANALOG INPUT 2
0.000
↓
MESSAGE
ANALOG INPUT 16
0.000