GE Multilin F35 Multiple Feeder Protection System 5-147
5 SETTINGS 5.6 CONTROL ELEMENTS
5
Figure 5–74: INCIPIENT CABLE FAULT DETECTOR SCHEME LOGIC
5.6.10 TRIP BUS
PATH: SETTINGS ÖØ CONTROL ELEMENTS ÖØ TRIP BUS ÖØ TRIP BUS 1(6)
TRIP BUS 1
TRIP BUS 1
FUNCTION: Disabled
Range: Enabled, Disabled
MESSAGE
TRIP BUS 1 BLOCK:
Off
Range: FlexLogic™ operand
MESSAGE
TRIP BUS 1 PICKUP
DELAY: 0.00 s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
TRIP BUS 1 RESET
DELAY: 0.00 s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
TRIP BUS 1 INPUT 1:
Off
Range: FlexLogic™ operand
MESSAGE
TRIP BUS 1 INPUT 2:
Off
Range: FlexLogic™ operand
MESSAGE
TRIP BUS 1 INPUT 16:
Off
Range: FlexLogic™ operand
MESSAGE
TRIP BUS 1
LATCHING: Disabled
Range: Enabled, Disabled
MESSAGE
TRIP BUS 1 RESET:
Off
Range: FlexLogic™ operand
MESSAGE
TRIP BUS 1 TARGET:
Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
TRIP BUS 1
EVENTS: Disabled
Range: Enabled, Disabled
Detection logic
SETTING
= Enabled
= Disabled
INCIPIENT FAULT 1 FUNCTION
SETTING
= OFF
INCIPIENT FAULT 1 BLOCK
SETTING
=IA
=IB
INCIPIENT FAULT 1 SOURCE
=IC
=IN
AND
SETTING
INCIPIENT FAULT 1
PICKUP
RUN
> PICKUP
where is 2 cycles old
I
mag
´
I
I
mag
mag
´
SETTINGS
INCIPNT FLT 1 DETECT
WINDOW
RUN
INCIPIENT FLT 1 TRIP
COUNTS NUMBER
INCIPNT FLT 1 MODE
T
WINDOW
SETTINGS
INCIPIENT FAULT 1
RESET DELAY
0
T
RST
0
T
RST
0
T
RST
FLEXLOGIC OPERANDS
INCIPNT FLT 1 OP A
INCIPNT FLT 1 OP B
INCIPNT FLT 1 OP C
INCIPNT FLT 1 OP
OR
FLEXLOGIC OPERANDS
INCIPNT FLT 1 PKP A
INCIPNT FLT 1 BPKP
INCIPNT FLT 1 CPKP
INCIPNT FLT 1 PKP
OR
ACTUAL VALUES
INCIPIENT FAULT 1 PH B
FAULTS
INCIPIENT FAULT 1 PH A
FAULTS
INCIPIENT FAULT 1 PH C
FAULTS
COMMAND
=Yes
CLEAR INCIPIENT FAULT
COUNTERS
RESET
832028A1.CDR