GE Multilin F35 Multiple Feeder Protection System 5-87
5 SETTINGS 5.4 FLEXLOGIC™
5
ELEMENT:
Neutral
instantaneous
overcurrent
NEUTRAL IOC1 PKP
NEUTRAL IOC1 OP
NEUTRAL IOC1 DPO
Neutral instantaneous overcurrent 1 has picked up
Neutral instantaneous overcurrent 1 has operated
Neutral instantaneous overcurrent 1 has dropped out
NEUTRAL IOC2 to IOC12 Same set of operands as shown for NEUTRAL IOC1
ELEMENT:
Neutral overvoltage
NEUTRAL OV1 PKP
NEUTRAL OV1 DPO
NEUTRAL OV1 OP
Neutral overvoltage element 1 has picked up
Neutral overvoltage element 1 has dropped out
Neutral overvoltage element 1 has operated
ELEMENT:
Neutral time
overcurrent
NEUTRAL TOC1 PKP
NEUTRAL TOC1 OP
NEUTRAL TOC1 DPO
Neutral time overcurrent 1 has picked up
Neutral time overcurrent 1 has operated
Neutral time overcurrent 1 has dropped out
NEUTRAL TOC2 to TOC6 Same set of operands as shown for NEUTRAL TOC1
ELEMENT:
Phase
instantaneous
overcurrent
PHASE IOC1 PKP
PHASE IOC1 OP
PHASE IOC1 DPO
PHASE IOC1 PKP A
PHASE IOC1 PKP B
PHASE IOC1 PKP C
PHASE IOC1 OP A
PHASE IOC1 OP B
PHASE IOC1 OP C
PHASE IOC1 DPO A
PHASE IOC1 DPO B
PHASE IOC1 DPO C
At least one phase of phase instantaneous overcurrent 1 has picked up
At least one phase of phase instantaneous overcurrent 1 has operated
At least one phase of phase instantaneous overcurrent 1 has dropped out
Phase A of phase instantaneous overcurrent 1 has picked up
Phase B of phase instantaneous overcurrent 1 has picked up
Phase C of phase instantaneous overcurrent 1 has picked up
Phase A of phase instantaneous overcurrent 1 has operated
Phase B of phase instantaneous overcurrent 1 has operated
Phase C of phase instantaneous overcurrent 1 has operated
Phase A of phase instantaneous overcurrent 1 has dropped out
Phase B of phase instantaneous overcurrent 1 has dropped out
Phase C of phase instantaneous overcurrent 1 has dropped out
PHASE IOC2 to IOC12 Same set of operands as shown for PHASE IOC1
ELEMENT:
Phase time
overcurrent
PHASE TOC1 PKP
PHASE TOC1 OP
PHASE TOC1 DPO
PHASE TOC1 PKP A
PHASE TOC1 PKP B
PHASE TOC1 PKP C
PHASE TOC1 OP A
PHASE TOC1 OP B
PHASE TOC1 OP C
PHASE TOC1 DPO A
PHASE TOC1 DPO B
PHASE TOC1 DPO C
At least one phase of phase time overcurrent 1 has picked up
At least one phase of phase time overcurrent 1 has operated
At least one phase of phase time overcurrent 1 has dropped out
Phase A of phase time overcurrent 1 has picked up
Phase B of phase time overcurrent 1 has picked up
Phase C of phase time overcurrent 1 has picked up
Phase A of phase time overcurrent 1 has operated
Phase B of phase time overcurrent 1 has operated
Phase C of phase time overcurrent 1 has operated
Phase A of phase time overcurrent 1 has dropped out
Phase B of phase time overcurrent 1 has dropped out
Phase C of phase time overcurrent 1 has dropped out
PHASE TOC2 to TOC6 Same set of operands as shown for PHASE TOC1
ELEMENT:
Phase undervoltage
PHASE UV1 PKP
PHASE UV1 OP
PHASE UV1 DPO
PHASE UV1 PKP A
PHASE UV1 PKP B
PHASE UV1 PKP C
PHASE UV1 OP A
PHASE UV1 OP B
PHASE UV1 OP C
PHASE UV1 DPO A
PHASE UV1 DPO B
PHASE UV1 DPO C
At least one phase of phase undervoltage 1 has picked up
At least one phase of phase undervoltage 1 has operated
At least one phase of phase undervoltage 1 has dropped out
Phase A of phase undervoltage 1 has picked up
Phase B of phase undervoltage 1 has picked up
Phase C of phase undervoltage 1 has picked up
Phase A of phase undervoltage 1 has operated
Phase B of phase undervoltage 1 has operated
Phase C of phase undervoltage 1 has operated
Phase A of phase undervoltage 1 has dropped out
Phase B of phase undervoltage 1 has dropped out
Phase C of phase undervoltage 1 has dropped out
PHASE UV2 Same set of operands as shown for PHASE UV1
ELEMENT:
Selector switch
SELECTOR 1 POS Y
SE
LECTOR 1 BIT 0
SELECTOR 1 BIT 1
SELECTOR 1 BIT 2
SELECTOR 1 STP ALARM
SELECTOR 1 BIT ALARM
SELECTOR 1 ALARM
SELECTOR 1 PWR ALARM
Selector switch 1 is in Position Y (mutually exclusive operands)
First bit of the 3-bit word encoding position of selector 1
Second bit of the 3-bit word encoding position of selector 1
Third bit of the 3-bit word encoding position of selector 1
Position of selector 1 has been pre-selected with the stepping up control
input but not acknowledged
Position of selector 1 has been pre-selected with the 3-bit control input but
not acknowledged
Position of selector 1 has been pre-selected but not acknowledged
Position of selector switch 1 is undetermined or restored from memory when
the relay powers up and synchronizes to the three-bit input
SELECTOR 2 Same set of operands as shown above for SELECTOR 1
ELEMENT:
Setting group
SETTING GROUP ACT 1
SETTING GROUP ACT 2
SETTING GROUP ACT 3
SETTING GROUP ACT 4
SETTING GROUP ACT 5
SETTING GROUP ACT 6
Setting group 1 is active
Setting group 2 is active
Setting group 3 is active
Setting group 4 is active
Setting group 5 is active
Setting group 6 is active
Table 5–7: F35 FLEXLOGIC™ OPERANDS (Sheet 3 of 6)
OPERAND TYPE OPERAND SYNTAX OPERAND DESCRIPTION

Table of Contents