GE Multilin F35 Multiple Feeder Protection System B-41
APPENDIX B B.4 MEMORY MAPPING
B
B0DA IEC 61850 MMXU A.phsC Deadband 1 0.001 to 100 % 0.001 F003 10000
B0DC IEC 61850 MMXU A.neut Deadband 1 0.001 to 100 % 0.001 F003 10000
B0DE IEC 61850 MMXU W.phsA Deadband 1 0.001 to 100 % 0.001 F003 10000
B0E0 IEC 61850 MMXU W.phsB Deadband 1 0.001 to 100 % 0.001 F003 10000
B0E2 IEC 61850 MMXU W.phsC Deadband 1 0.001 to 100 % 0.001 F003 10000
B0E4 IEC 61850 MMXU VAr.phsA Deadband 1 0.001 to 100 % 0.001 F003 10000
B0E6 IEC 61850 MMXU VAr.phsB Deadband 1 0.001 to 100 % 0.001 F003 10000
B0E8 IEC 61850 MMXU VAr.phsC Deadband 1 0.001 to 100 % 0.001 F003 10000
B0EA IEC 61850 MMXU VA.phsA Deadband 1 0.001 to 100 % 0.001 F003 10000
B0EC IEC 61850 MMXU VA.phsB Deadband 1 0.001 to 100 % 0.001 F003 10000
B0EE IEC 61850 MMXU VA.phsC Deadband 1 0.001 to 100 % 0.001 F003 10000
B0F0 IEC 61850 MMXU PF.phsA Deadband 1 0.001 to 100 % 0.001 F003 10000
B0F2 IEC 61850 MMXU PF.phsB Deadband 1 0.001 to 100 % 0.001 F003 10000
B0F4 IEC 61850 MMXU PF.phsC Deadband 1 0.001 to 100 % 0.001 F003 10000
B0F6 ...Repeated for Deadband 2
B12C ...Repeated for Deadband 3
B162 ...Repeated for Deadband 4
B198 ...Repeated for Deadband 5
B1CE ...Repeated for Deadband 6
IEC 61850 GGIO2 Control Configuration (Read/Write Setting) (64 modules)
B240 IEC 61850 GGIO2.CF.SPCSO1.ctlModel Value 0 to 2 --- 1 F001 2
B241 IEC 61850 GGIO2.CF.SPCSO2.ctlModel Value 0 to 2 --- 1 F001 2
B242 IEC 61850 GGIO2.CF.SPCSO3.ctlModel Value 0 to 2 --- 1 F001 2
B243 IEC 61850 GGIO2.CF.SPCSO4.ctlModel Value 0 to 2 --- 1 F001 2
B244 IEC 61850 GGIO2.CF.SPCSO5.ctlModel Value 0 to 2 --- 1 F001 2
B245 IEC 61850 GGIO2.CF.SPCSO6.ctlModel Value 0 to 2 --- 1 F001 2
B246 IEC 61850 GGIO2.CF.SPCSO7.ctlModel Value 0 to 2 --- 1 F001 2
B247 IEC 61850 GGIO2.CF.SPCSO8.ctlModel Value 0 to 2 --- 1 F001 2
B248 IEC 61850 GGIO2.CF.SPCSO9.ctlModel Value 0 to 2 --- 1 F001 2
B249 IEC 61850 GGIO2.CF.SPCSO10.ctlModel Value 0 to 2 --- 1 F001 2
B24A IEC 61850 GGIO2.CF.SPCSO11.ctlModel Value 0 to 2 --- 1 F001 2
B24B IEC 61850 GGIO2.CF.SPCSO12.ctlModel Value 0 to 2 --- 1 F001 2
B24C IEC 61850 GGIO2.CF.SPCSO13.ctlModel Value 0 to 2 --- 1 F001 2
B24D IEC 61850 GGIO2.CF.SPCSO14.ctlModel Value 0 to 2 --- 1 F001 2
B24E IEC 61850 GGIO2.CF.SPCSO15.ctlModel Value 0 to 2 --- 1 F001 2
B24F IEC 61850 GGIO2.CF.SPCSO16.ctlModel Value 0 to 2 --- 1 F001 2
B250 IEC 61850 GGIO2.CF.SPCSO17.ctlModel Value 0 to 2 --- 1 F001 2
B251 IEC 61850 GGIO2.CF.SPCSO18.ctlModel Value 0 to 2 --- 1 F001 2
B252 IEC 61850 GGIO2.CF.SPCSO19.ctlModel Value 0 to 2 --- 1 F001 2
B253 IEC 61850 GGIO2.CF.SPCSO20.ctlModel Value 0 to 2 --- 1 F001 2
B254 IEC 61850 GGIO2.CF.SPCSO21.ctlModel Value 0 to 2 --- 1 F001 2
B255 IEC 61850 GGIO2.CF.SPCSO22.ctlModel Value 0 to 2 --- 1 F001 2
B256 IEC 61850 GGIO2.CF.SPCSO23.ctlModel Value 0 to 2 --- 1 F001 2
B257 IEC 61850 GGIO2.CF.SPCSO24.ctlModel Value 0 to 2 --- 1 F001 2
B258 IEC 61850 GGIO2.CF.SPCSO25.ctlModel Value 0 to 2 --- 1 F001 2
B259 IEC 61850 GGIO2.CF.SPCSO26.ctlModel Value 0 to 2 --- 1 F001 2
B25A IEC 61850 GGIO2.CF.SPCSO27.ctlModel Value 0 to 2 --- 1 F001 2
B25B IEC 61850 GGIO2.CF.SPCSO28.ctlModel Value 0 to 2 --- 1 F001 2
B25C IEC 61850 GGIO2.CF.SPCSO29.ctlModel Value 0 to 2 --- 1 F001 2
B25D IEC 61850 GGIO2.CF.SPCSO30.ctlModel Value 0 to 2 --- 1 F001 2
B25E IEC 61850 GGIO2.CF.SPCSO31.ctlModel Value 0 to 2 --- 1 F001 2
B25F IEC 61850 GGIO2.CF.SPCSO32.ctlModel Value 0 to 2 --- 1 F001 2
B260 IEC 61850 GGIO2.CF.SPCSO33.ctlModel Value 0 to 2 --- 1 F001 2
B261 IEC 61850 GGIO2.CF.SPCSO34.ctlModel Value 0 to 2 --- 1 F001 2
Table B–9: MODBUS MEMORY MAP (Sheet 34 of 48)
ADDR REGISTER NAME RANGE UNITS STEP FORMAT DEFAULT