5 Commissioning
NOTICE
Shielding/extension of connecting cables
Warning to avoid damage to property
Apply shielded cables directly (without any intermediate terminals if at all possible).
If intermediate terminals are necessary, take the shortest route to applying the shielding
to the terminal.
Avoid long connecting wires without shielding.
Use a separate, shielded extension cable to implement an extension on site.
NOTICE
High electromagnetic interference
Excessive electromagnetic interference can lead to sporadic problems with flame detection
and even prevent it.
Connect chassis earth (earthing bolt at the device) to functional earth (FPE).
It is a connection between the mass of the supply voltage and FPE prepared.
NOTICE
EMC emission testing
It was ascertained during the type test that the device meets the EMC emissions require-
ments. A separate EMC emissions test is not necessary after installation.
5.1.2 Electrical Safety – Requirements to Be Met by Third-party Manufacturers
DANGER!
Analogue output current loop - Protection against electric shock
Measuring circuits must be separated safely to dangerous active parts according to EN 61140
„Protection against electric shock …“.
You achieve this by double or reinforced isolation according to EN 61010-1 „Safety re-
quirements for electrical equipment for measurement, control and laboratory use“.
WARNING!
Radio interference suppression of the output contacts
In the interests of safety, ensure when installing the output contacts that:
The user suppresses radio interference in such a way that the contacts of the safety relay
contact output cannot be shorted by defective components of the suppressor circuitry.