GE Multilin F35 Multiple Feeder Protection System 5-149
5 SETTINGS 5.6 CONTROL ELEMENTS
5
Figure 5–76: TRIP BUS LOGIC
***
SETTINGS
=Off
TRIP BUS 1 INPUT 2
=Off
TRIP BUS 1 INPUT 1
=Off
TRIP BUS 1 INPUT 16
OR
SETTINGS
= Enabled
TRIP BUS 1
FUNCTION
=Off
TRIP BUS 1 BLOCK
AND
AND
Latch
S
R
Non-volatile,
set-dominant
SETTINGS
= Enabled
TRIP BUS 1
LATCHING
=Off
TRIP BUS 1 RESET
FLEXLOGIC OPERAND
TRIP BUS 1 PKP
OR
SETTINGS
TRIP BUS 1 PICKUP
DELAY
TRIP BUS 1 RESET
DELAY
T
PKP
T
RST
FLEXLOGIC OPERAND
RESET OP
FLEXLOGIC OPERAND
TRIP BUS 1 OP
842023A1.CDR