GE Multilin F35 Multiple Feeder Protection System B-27
APPENDIX B B.4 MEMORY MAPPING
B
5D50 ...Repeated for Ground Time Overcurrent 6
Ground Instantaneous Overcurrent (Read/Write Grouped Setting) (12 modules)
5E00 Ground Instantaneous Overcurrent 1 Signal Source 0 to 5 --- 1 F167 0 (SRC 1)
5E01 Ground Instantaneous Overcurrent 1 Function 0 to 1 --- 1 F102 0 (Disabled)
5E02 Ground Instantaneous Overcurrent 1 Pickup 0 to 30 pu 0.001 F001 1000
5E03 Ground Instantaneous Overcurrent 1 Delay 0 to 600 s 0.01 F001 0
5E04 Ground Instantaneous Overcurrent 1 Reset Delay 0 to 600 s 0.01 F001 0
5E05 Ground Instantaneous Overcurrent 1 Block 0 to 65535 --- 1 F300 0
5E06 Ground Instantaneous Overcurrent 1 Target 0 to 2 --- 1 F109 0 (Self-reset)
5E07 Ground Instantaneous Overcurrent 1 Events 0 to 1 --- 1 F102 0 (Disabled)
5E08 Reserved (8 items) 0 to 1 --- 1 F001 0
5E10 ...Repeated for Ground Instantaneous Overcurrent 2
5E20 ...Repeated for Ground Instantaneous Overcurrent 3
5E30 ...Repeated for Ground Instantaneous Overcurrent 4
5E40 ...Repeated for Ground Instantaneous Overcurrent 5
5E50 ...Repeated for Ground Instantaneous Overcurrent 6
5E60 ...Repeated for Ground Instantaneous Overcurrent 7
5E70 ...Repeated for Ground Instantaneous Overcurrent 8
5E80 ...Repeated for Ground Instantaneous Overcurrent 9
5E90 ...Repeated for Ground Instantaneous Overcurrent 10
5EA0 ...Repeated for Ground Instantaneous Overcurrent 11
5EB0 ...Repeated for Ground Instantaneous Overcurrent 12
Incipient cable fault detector actual values (read only)
5EC0 Incipient cable fault detector 1 phase A counter 0 to 65535 --- 1 F001 0
5EC1 Incipient cable fault detector 1 phase B counter 0 to 65535 --- 1 F001 0
5EC2 Incipient cable fault detector 1 phase C counter 0 to 65535 --- 1 F001 0
5EC3 ...Repeated for incipient cable fault detector 2
5EC6 ...Repeated for incipient cable fault detector 3
5EC9 ...Repeated for incipient cable fault detector 4
5ECC ...Repeated for incipient cable fault detector 5
5ECF ...Repeated for incipient cable fault detector 6
Setting Groups (Read/Write Setting)
5F80 Setting Group for Modbus Comms (0 means group 1) 0 to 5 --- 1 F001 0
5F81 Setting Groups Block 0 to 65535 --- 1 F300 0
5F82 FlexLogic to Activate Groups 2 through 6 (5 items) 0 to 65535 --- 1 F300 0
5F89 Setting Group Function 0 to 1 --- 1 F102 0 (Disabled)
5F8A Setting Group Events 0 to 1 --- 1 F102 0 (Disabled)
Setting Groups (Read Only)
5F8B Current Setting Group 0 to 5 --- 1 F001 0
Setting Group Names (Read/Write Setting)
5F8C Setting Group 1 Name --- --- --- F203 (none)
5F94 Setting Group 2 Name --- --- --- F203 (none)
5F9C Setting Group 3 Name --- --- --- F203 (none)
5FA4 Setting Group 4 Name --- --- --- F203 (none)
5FAC Setting Group 5 Name --- --- --- F203 (none)
5FB4 Setting Group 6 Name --- --- --- F203 (none)
Autoreclose (Read/Write Setting) (6 modules)
6240 Autoreclose 1 Function 0 to 1 --- 1 F102 0 (Disabled)
6241 Autoreclose 1 Initiate 0 to 65535 --- 1 F300 0
6242 Autoreclose 1 Block 0 to 65535 --- 1 F300 0
6243 Autoreclose 1 Max Number of Shots 1 to 4 --- 1 F001 1
6244 Autoreclose 1 Manual Close 0 to 65535 --- 1 F300 0
6245 Autoreclose 1 Manual Reset from LO 0 to 65535 --- 1 F300 0
6246 Autoreclose 1 Reset Lockout if Breaker Closed 0 to 1 --- 1 F108 0 (Off)
Table B–9: MODBUS MEMORY MAP (Sheet 20 of 48)
ADDR REGISTER NAME RANGE UNITS STEP FORMAT DEFAULT