EasyManua.ls Logo

YASKAWA F7

YASKAWA F7
202 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Loading...
Programming 57
equation to calculate the motor rated slip frequency based on motor nameplate data:
E2-03 No Load Current
Setting Range: Model Dependent
Factory Default: Model Dependent
Set E2-03 to the motor no-load current at rated voltage and rated frequency. If the rotational Auto-tuning operation completes
successfully (T1-02 = 0), this value is automatically calculated. Consult the motor manufacturer for the proper value if the no
load current is not stated on the motor nameplate.
E2-04 Number of Motor Poles
Setting Range: 2 to 48
Factory Default: 4
This parameter sets the number of motor poles. During auto-tuning, it is required for the operator to enter the number of motor
poles (T1-06) in the Auto-Tuning menu. If the Auto-tuning operation completes successfully (T1-02 = 0, 1, or 2), the value
entered into T1-06 will automatically be written into E2-04.
E2-05 Motor Line-to-Line Resistance
Setting Range: 0.0000to 65.000 Ω
Factory Default: 9.842 Ω
Sets the line-to-line resistance of the motors stator winding. If the Auto-tuning operation completes successfully (T1-02 = 0, 1,
or 2), this value is automatically calculated. Remember this value must be entered as line-line and not line neutral.
E2-06 Motor Leakage Inductance
Setting Range: 0.0 to 40.0 %
Factory Default: Model Dependent
Sets the voltage drop due to motor leakage inductance as a percentage of motor rated voltage. If the rotational Auto-tuning
operation completes successfully (T1-02 = 0), this value is automatically calculated.
E2-07 Motor Iron-core Saturation Coefficient 1
Setting Range: 0.00 to 0.50
Factory Default: 0.50
This parameter sets the motor iron saturation coefficient at 50% of the magnetic flux. If the rotational Auto-tuning operation
completes successfully (T1-02 = 0), this value is automatically calculated.
where:
f
s
f
NP()
120
-----------------=
f
s
: slip frequency (Hz)
f : rated frequency (Hz)
N : rated motor speed (rpm)
P : number of motor poles
Phase-to-phase Resistance at
Insulation Class Temperature
273 + (25 + insulation class temperature) /2
273 + insulation class temperature
E2-05=
)
(
X
Where: Insulation class temperature is in °C

Other manuals for YASKAWA F7

Related product manuals