Page #70 background imageLoading...
Page #70 background image
Programming 62
E4-06 Motor 2 Leakage Inductance
Setting Range: 0.0 to 40.0 %
Factory Default: Model Dependent
Sets the voltage drop due to motor leakage inductance as a percentage of motor rated voltage. If the rotational Auto-tuning
operation completes successfully (T1-02 = 0), this value is automatically calculated.
E4-07 Motor Rated Output
Setting Range: 0.00 to 650.00 kW
Factory Default: Model Dependent
This parameter sets the motor rated power in kilowatts (kW). If the rotational Auto-tuning operation completes successfully
(T1-02 = 0), this value is automatically calculated.
F1 PG Option Setup
F1-01 PG Pulses / Revolution
Setting Range: 0 to 60000
Factory Default: 1024
This parameter sets the number of PG pulses per one revolution of the encoder (pulse generator) when using PG option board
on the Drive.
F1-02 Operation Selection at PG Open Circuit (PGO)
This parameter sets the stopping method when a PG open circuit fault (PGO) occurs according to the PGO detection time set in
parameter F1-14.
F1-03 Operation Selection at Overspeed (OS)
This parameter sets the stopping method when a overspeed fault (OS) occurs according to the OS detection level and detection
time set in parameter F1-08 and F1-09, respectively.
Setting Description
0 Ramp to Stop - Decelerate to stop using active deceleration time.
1 Coast to Stop (factory default)
2 Fast-stop - Decelerate to stop using the deceleration time in C1-09.
3 Alarm Only - Drive continues operation.
Setting Description
0 Ramp to Stop - Decelerate to stop using active deceleration time.
1 Coast to Stop (factory default)
2 Fast-stop - Decelerate to stop using the deceleration time in C1-09.
3 Alarm Only - Drive continues operation.

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC

Related product manuals