Programming 61
The Motor Rated Current parameter (E2-01) is used by the Drive to protect the motor and for proper Vector control when
using Open Loop Vector or Flux Vector control methods (E3-01 = 2 or 3). The motor protection parameter L1-01 is enabled by
default. Set E2-01 to the full load amps (FLA) stamped on the motors nameplate.
During Auto-tuning, it is required for the operator to enter the motors rated current (T1-04) in the Auto-Tuning menu. If the
Auto-tuning operation completes successfully (T1-02 = 0), the value entered into T1-04 will automatically be written into E4-
01.
E4-02 Motor 2 Rated Slip
Setting Range: Model Dependent
Factory Default: Model Dependent
This parameter sets the motor rated slip frequency in units of 0.01Hz. If the rotational Auto-tuning operation completes
successfully, this value is automatically calculated. The default setting varies depending on the drive model number (o2-04).
The following equation to calculate the motor rated slip frequency based on motor nameplate data:
E4-03 Motor 2 No Load Current
Setting Range: Model Dependent
Factory Default: Model Dependent
Set E4-03 to the motor no-load current at rated voltage and rated frequency. If the rotational Auto-tuning operation completes
successfully (T1-02 = 0), this value is automatically calculated. Consult the motor manufacturer for the proper value if the no
load current is not stated on the motor nameplate.
E4-04 Motor 2 Number of Poles
Setting Range: 2 to 48
Factory Default: 4
This parameter sets the number of motor poles. During auto-tuning, it is required for the operator to enter the number of motor
poles (T1-06) in the Auto-Tuning menu. If the Auto-tuning operation completes successfully (T1-02 = 0, 1, or 2), the value
entered into T1-06 will automatically be written into E4-04.
E4-05 Motor 2 Line-to-Line Resistance
Setting Range: 0.0000to 65.000 Ω
Factory Default: 9.842 Ω
Sets the line-to-line resistance of the motors stator winding. If the Auto-tuning operation completes successfully (T1-02 = 0,
1, or 2), this value is automatically calculated. Remember this value must be entered as line-line and not line neutral.
where:
f
s
f
NP()
120
-----------------
=
f
s
: slip frequency (Hz)
f : rated frequency (Hz)
N : rated motor speed (rpm)
P : number of motor poles
Phase-to-phase Resistance at
Insulation Class Temperature
273 + (25 + insulation class temperature) /2
273 + insulation class temperature
E2-05=
)
(
X
Where: Insulation class temperature is in °C

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC

Related product manuals