Programming 82
Function: PID SFS Cancel
Setting: 34
SFS means softstart, also referred to as accel/decel in this description.
By configuring a digital input as a PID SFS (softstart) Cancel input (H1-0x= 34), the operator will be able to use a contact closure to
remove the acceleration and deceleration times that are applied to changes in the PID setpoint by the b5-17 parameter. If the digital
input configured as PID SFS Cancel is closed, the PID setpoint Accel/Decel (Parameter b5-17) will be ignored. Immediate updating
of any change to the setpoint will apply.
Function: Input Level Selection
Setting: 35
When using the PID Function built into the Drive, the chosen set point is compared with the measured feedback. The difference is
called the Error. The proportional and integral function are applied to this error. For some applications it may be appropriate to invert
the input to the PID block. This can be accomplished by setting one of the digital inputs up as an Input Level Sel (H1-0x=35). When
an Input Level Sel digital input is closed the Error will be inverted before it is passed to the PID block.
Fig. 52 PID Error signal Inversion Block Diagram
Function: DC Injection Braking
Setting: 60
When a DC injection braking command is input while the Drive is stopped, DC injection braking operation is activated. When
a run command or a jog command is input, DC injection braking is released to start operation (jog operation has priority).
Fig. 53 DC Injection Braking Input Timing Diagram
Set
Point
+
-
Z
-
1
PI Block
Feed
back
H1=0x=35
OP
CLOSED
Open
Closed
PID Block
DC Injection Braking Command
Fwd Run Command
ON
OFF
OFF
Output Frequency
ON
OFF
OFF
DC Injection
Braking
DC Injection
Braking
DC Injection Braking
Start Frequency
(B2-01)

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC

Related product manuals