GE Multilin F35 Multiple Feeder Protection System B-21
APPENDIX B B.4 MEMORY MAPPING
B
4448 User Programmable IRIG-B Fail Function 0 to 1 --- 1 F102 1 (Enabled)
4449 User Programmable Ethernet Switch Fail Function 0 to 1 --- 1 F102 0 (Disabled)
CT Settings (Read/Write Setting) (6 modules)
4480 Phase CT 1 Primary 1 to 65000 A 1 F001 1
4481 Phase CT 1 Secondary 0 to 1 --- 1 F123 0 (1 A)
4482 Ground CT 1 Primary 1 to 65000 A 1 F001 1
4483 Ground CT 1 Secondary 0 to 1 --- 1 F123 0 (1 A)
4484 ...Repeated for CT Bank 2
4488 ...Repeated for CT Bank 3
448C ...Repeated for CT Bank 4
4490 ...Repeated for CT Bank 5
4494 ...Repeated for CT Bank 6
VT Settings (Read/Write Setting) (3 modules)
4500 Phase VT 1 Connection 0 to 1 --- 1 F100 0 (Wye)
4501 Phase VT 1 Secondary 50 to 240 V 0.1 F001 664
4502 Phase VT 1 Ratio 1 to 24000 :1 1 F060 1
4504 Auxiliary VT 1 Connection 0 to 6 --- 1 F166 1 (Vag)
4505 Auxiliary VT 1 Secondary 50 to 240 V 0.1 F001 664
4506 Auxiliary VT 1 Ratio 1 to 24000 :1 1 F060 1
4508 ...Repeated for VT Bank 2
4510 ...Repeated for VT Bank 3
Source Settings (Read/Write Setting) (6 modules)
4580 Source 1 Name --- --- --- F206 “SRC 1"
4583 Source 1 Phase CT 0 to 63 --- 1 F400 0
4584 Source 1 Ground CT 0 to 63 --- 1 F400 0
4585 Source 1 Phase VT 0 to 63 --- 1 F400 0
4586 Source 1 Auxiliary VT 0 to 63 --- 1 F400 0
4587 ...Repeated for Source 2
458E ...Repeated for Source 3
4595 ...Repeated for Source 4
459C ...Repeated for Source 5
45A3 ...Repeated for Source 6
Power System (Read/Write Setting)
4600 Nominal Frequency 25 to 60 Hz 1 F001 60
4601 Phase Rotation 0 to 1 --- 1 F106 0 (ABC)
4602 Frequency And Phase Reference 0 to 5 --- 1 F167 0 (SRC 1)
4603 Frequency Tracking Function 0 to 1 --- 1 F102 1 (Enabled)
Incipient cable fault detector (read/write settings)
46B2 Incipient cable fault detector 1 function 0 to 1 --- 1 F102 0 (Disabled)
46B3 Incipient cable fault detector 1 block 0 to 65535 --- 1 F300 0
46B4 Incipient cable fault detector 1 source 0 to 5 --- 1 F167 0 (SRC 1)
46B5 Incipient cable fault detector 1 pickup 0.1 to 10 pu 0.01 F001 50
46B6 Incipient cable fault detector 1 mode 0 to 1 --- 1 F254 0 (Number of Counts)
46B7 Incipient cable fault detector 1 counts 1 to 10 --- 1 F001 2
46B8 Incipient cable fault detector 1 time window 0 to 1000 s 0.01 F003 1000
46BA Incipient cable fault detector 1 reset delay 0 to 65.535 s 0.001 F001 100
46BB Incipient cable fault detector 1 target 0 to 2 --- 1 F109 0 (Self-reset)
46BC Incipient cable fault detector 1 events 0 to 1 --- 1 F102 0 (Disabled)
46BD ...Repeated for incipient cable fault detector 2
46C8 ...Repeated for incipient cable fault detector 3
46D3 ...Repeated for incipient cable fault detector 4
46DE ...Repeated for incipient cable fault detector 5
46E9 ...Repeated for incipient cable fault detector 6
Table B–9: MODBUS MEMORY MAP (Sheet 14 of 48)
ADDR REGISTER NAME RANGE UNITS STEP FORMAT DEFAULT