5-8 F650 Digital Bay Controller GEK-106310AB
5.2 PRODUCT SETUP 5 SETTINGS
5
5.2.3 FAULT REPORT
5.2.3.1 OVERVIEW
The fault report module defines the type of fault (three-phase, phase-to-phase, phase-to-ground), and the distance to the
fault. The fault activation signal (FAULT REPORT TRIGG) is programmed at “Setpoint > Relay Configuration >
Protection Elements”.
The fault report provides fault date, fault type and fault location information.
Information referred to the last ten faults is stored as fault report and available to the user through the EnerVista 650 Setup
software or the web server application. Each fault report includes the following information:
Fault date and time
Pre-fault current and voltage in primary values
Fault current and voltages in primary values
•Fault type
Distance to the fault (fault location)
Line parameters
Recloser and breaker status information
As an option, the Relay offers the possibility to display a fault-warning message on the relay HMI (selectable by setting).
5.2.3.2 FAULT REPORT SETTINGS
Table 5–9: FAULT REPORT SETTINGS
Function permission (Function): Enabling this setting allows to create a fault report when the FAULT REPORT TRIGG is
activated.
Positive sequence impedance module (Pos Seq Module): Value, in ohms, of the line positive sequence
impedance module.
Positive sequence impedance Angle (Pos Seq Angle): Value, in degrees, of the line positive sequence angle.
Zero sequence impedance module (Zero Seq Module): Value, in ohms, of the line zero sequence impedance
module.
Zero sequence impedance Angle (Zero Seq Angle): Value, in degrees, of the line zero sequence angle.
Line Length: The metering element can be kilometers or miles.
Show Fault On HMI: This setting enables or disables the option to display
faults on the Relay HMI.
Snapshot Events: This setting enables or disables the snapshot event
generation for the fault report element.
SETPOINT > PRODUCT SETUP > FAULT REPORT
Setting Description Name Default Value Step Range
Function permission Function DISABLED N/A [DISABLED – ENABLED]
Positive sequence impedance module Pos Seq Module 3.00 0.01 Ohm [0.01 : 250.00]
Positive sequence impedance angle Pos Seq Angle 75 1 Deg [25 : 90]
Zero sequence impedance module Zero Seq Module 9.00 0.01 Ohm [0.01 : 750.00]
Zero sequence impedance angle Zero Seq Angle 75 1 Deg [25 : 90]
Line length Line Length 100.0 0.1 [0.0 : 2000.0]
Display fault on HMI Show Fault On HMI DISABLED N/A [DISABLED – ENABLED]
Snapshot Event generation Snapshot Events ENABLED N/A [DISABLED – ENABLED]