10-12 F650 Digital Bay Controller GEK-106310AB
10.9 INPUTS AND OUTPUTS 10 COMMISSIONING
10
10.9.2 CONTACT OUTPUTS
The correct activation of every output will be verified.
For every output, activation command of a single contact must be given, and then verify that only that contact is activated.
Go to EnerVista 650 Setup Software (Setpoint>Inputs/Outputs>Force Outputs).
For switched contacts, the change of state of both contacts shall be verified.
10.9.3 CIRCUIT CONTINUITY SUPERVISION INPUTS
Supervision inputs will be tested as normal inputs, revising the voltage level that will be 19 Volts.
Coil 1:
Apply 19 Vdc to both 52/a (terminals F1-F2) and 52/b (terminals F3-F4)”Coil 1” circuit supervision inputs and verify that
they are activated.
Apply -19 Vdc to both 52/a (terminals F1-F2) and 52/b (terminals F3-F4)”Coil 1” circuit supervision inputs and verify
that they are activated.
Remove voltage from both inputs and verify that it takes them 500 ms to change state (deactivate).
Coil 2:
Apply 19 Vdc to both 52/a (terminals F15-F16) and 52/b (terminals F17-F18)”Coil 2” circuit supervision inputs and
verify that they are activated.
Apply -19 Vdc to both 52/a (terminals F15-F16) and 52/b (terminals F17-F18)”Coil 2” circuit supervision inputs and
verify that they are activated.
Remove voltage from both inputs and verify that it takes them 500 ms to change state (deactivate).
10.9.4 LATCHING CIRCUITS
Send a closing command to the latched contact (F31-F33).
Make circulate a current of 500 mA through the contact in series with the sensing terminal.
Send an opening command and verify that the contact does not open.
Interrupt current and check that the contact is released.
Repeat the test for the other latched contact (F34-F36).
I
500

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC

Related product manuals