5-110 F650 Digital Bay Controller GEK-106310AB
5.5 CONTROL ELEMENTS 5 SETTINGS
5
The signals related to the locked rotor pickups and operations for the three locked rotor elements can be viewed at Actual
> Status > Control Elements > Locked Rotor and they are as follows:
Table 5–88: LOCKED ROTOR STATUS
The block signals for the locked rotor element can be configured at: Setpoint > Relay Configuration > Protection
Elements
Table 5–89: LOCKED ROTOR BLOCKS
Note:
The element works with primary values.
The element will pickup if at least one of the three phase currents is above the adjusted level. The operation value will be
the higher of the three.
The reset level is 97% to 98% of the pickup level.
5.5.10 PULSE COUNTERS
The F650 includes eight pulse counters, each pulse counter stores the activation number of the input set to that pulse
counter. This value can be multiplied for a factor selectable by setting.
The inputs used in this pulse counter function can be selected from all the available in the F650 device. Take into account
that the input/output settings are both set for the generic input as well as for the pulse counter input, e.g. Debounce time.
The settings for this function can be found at Setpoint > Control Elements > Pulse Counters
Table 5–90: PULSE COUNTERS SETTINGS
Pulse Counters settings are:
CntPulses Enabled: Enable/disable each pulse counter.
CntPulses Name: Each pulse counter can have a configurable user name.
LOCKED ROTOR STATUS
LOCKED ROTOR1 PKP
LOCKED ROTOR1 OP
LOCKED ROTOR2 PKP
LOCKED ROTOR2 OP
LOCKED ROTOR3 PKP
LOCKED ROTOR3 OP
LOCKED ROTOR BLOCKS
LOCKED ROTOR1 BLK
LOCKED ROTOR2 BLK
LOCKED ROTOR3 BLK
SETPOINT > CONTROL ELEMENTS > PULSE COUNTERS
SETTING DESCRIPTION NAME DEFAULT VALUE STEP RANGE
Pulse counter enabling setting CntPulses Enabled X DISABLED N/A [DISABLED – ENABLED]
Name of the pulse counter CntPulses Name X Pulse Counter X N/A N/A
Multiplier factor for the pulse counter CntPulses Factor X 1.000 0.001 [0.000 : 65000.000]
Overflow value for the pulse counter CntPulses Overflow X 65535 1 [0 : 1000000]
Board selection for the pulse counter CntPulses Board Origin X F N/A [F,G,H,I]
Input index inside the selected board CntPulses Input Origin X 1 1 [1 : 32]
Note: X is the pulse counter index, up to 8.

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC