GEK-106310AB F650 Digital Bay Controller 5-33
5 SETTINGS 5.4 PROTECTION ELEMENTS
5
The distribution of protection elements in tabled groups is described in Table 5–28:
Table 5–28: DISTRIBUTION OF PROTECTION AND CONTROL ELEMENTS
The settings used for setting table management are located in Setpoint >Control Elements > Setting Group:
Table 5–29: SETTING GROUP SETTINGS
Setting Group settings are as follows:
Function: Possible values are: [DISABLED – ENABLED]
TABLE 1 TABLE 2 TABLE 3
1x50PH 1x50PH 1x50PH
1x50PL 1x50PL 1x50PL
1x50N 1x50N 1x50N
1x50G 1x50G 1x50G
1x50SG 1x50SG 1x50SG
1x50IG 1x50IG 1x50IG
1x51PH 1x51PH 1x51PH
1x51PL 1x51PL 1x51PL
1x51N 1x51N 1x51N
1x51G 1x51G 1x51G
1x51SG 1x51SG 1x51SG
1x46P 1x46P 1x46P
1x49P 1x49P 1x49P
1x67P 1x67P 1x67P
1x67N 1x67N 1x67N
1x67G 1x67G 1x67G
1x67SG 1x67SG 1x67SG
1x27P 1x27P 1x27P
1x59P 1x59P 1x59P
1x47P 1x47P 1x47P
1x59NH 1x59NH 1x59NH
1x59NL 1x59NL 1x59NL
1x59X 1x59X 1x59X
1x27X 1x27X 1x27X
1x32FP 1x32FP 1x32FP
1x32 1x32 1x32
1x32N High 1x32N High 1x32N High
1x32N Low 1x32N Low 1x32N Low
1x81U 1x81U 1x81U
1x81O 1x81O 1x81O
1 x Broken conductor 1 x Broken conductor 1 x Broken conductor
1 x Locked Rotor 1 x Locked Rotor 1 x Locked Rotor
1 x Freq. Rate of Change 1 x Fq. Rate of Change 1 x Fq. Rate of Change
1 x Load Encroachment 1 x Load Encroachment 1 x Load Encroachment
SETPOINT > CONTROL ELEMENTS > SETTING GROUP
Setting Description Name Default Value Step Range
Setting Grouping Permission Function DISABLED N/A [DISABLED – ENABLED]
Active Group Active Group GROUP 1 N/A [GROUP 1 – GROUP 2 – GROUP 3]
Snapshot Event generation Snapshot Events ENABLED N/A [DISABLED – ENABLED]